Here is part of an email from FM concerning a processing plant we did in 2010. 
I hope it helps.

"The major change in this submittal involved replacing suppression mode 
sprinklers over the process mezzanine with control mode sprinklers. The spacing 
of the sprinklers appears to be the same as the previous design. The sprinkler 
systems in the process area are now designed as follows (most demanding design 
listed):

Process and Bale Storage Area: 
Two sprinkler designs are used in this area. Early suppression fast response 
(ESFR), or suppression mode sprinklers protect the majority of the space. 
Control mode density area (CMDA), non-storage sprinklers are used to protect 
the process area mezzanine. 

ESFR Design:
12 heads + 2 @ 63 psi each, requiring 2,194 gpm @ 141.8 psi at the pump 
discharge.
Sprinklers are Tyco SIN # TY7226, ESFR, K = 16.8. 214°F, FM Approved heads. The 
maximum head spacing is 10 ft. by 10 ft. The calculations allow for a 250 gpm 
hose stream allowance.

CMDA Design:
0.50 gpm/sq.ft. / 3,000 sq.ft. requiring 2,239 gpm @ 81.5 psi at the pump 
discharge.
Sprinklers are Tyco SIN # TY5151, SR, K = 11.2. 200°F, pendent, FM Approved 
heads. The maximum area per head is 93 sq.ft. The calculations allow for a 500 
gpm hose stream allowance.

Credit is being given (contingent to compliance with the requirements listed 
below) to the structural beam that runs along column line G as a ceiling 
barrier for the purpose of separating the control mode and suppression mode 
sprinklers. This beam reportedly meets the following requirements:
1)      The beam is noncombustible, solid, and extends at least 2 ft. below the 
roof deck.
2)      The beam fits tightly against the underside of the roof. Openings 
created by ribs in the metal roof deck are not a concern, but openings created 
by channels between purlins or other structural members should be sealed. 4 ft. 
of clear space should be maintained, centered below the beam. 

There is no ceiling barrier separating the control mode from the ESFR 
sprinklers on the east side of the mezzanine. Since no ceiling barrier is 
present, the ESFR sprinklers were extended approximately 22 ft. west of 
gridline 13 into the process mezzanine area.

A full height demising wall is located along gridline 7 and will serve to 
separate the control mode sprinkles protection from the occupancy on the west 
side of the wall. The north wall of structure is located along column line B."

Ron F

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Roland Huggins
Sent: Tuesday, March 12, 2013 7:21 AM
To: [email protected]
Subject: Re: single stream recycling

but also lend itself to a smoldering / burrowing fire might make it worth a 
bump-up in the density

Roland

On Mar 12, 2013, at 5:09 AM, Matt Grise <[email protected]> wrote:

> we figured it would be similar to a closed array pile. Since it is all loose 
> trash, it is hard for air to get to the interior.
> 
> Matt Grisé PE*, LEED AP, NICET II  
> Sales Engineer 
> Alliance Fire Protection 

-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20130312/39fd98db/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to