I found this as a result of the phantom flow thread. 16.2.3.5 requires up to 
two additional sprinklers under obstructions be calc'd for a total of 14 
ESFR's. 22.4.4.6.4 says not to include ESFR's under obstructions. Seems like a 
correlating problem?

Ron F