Good morning from Santa Fe...Mr. Peck's response is 'spot-on'. Lab testing 
has shown sprinklers (horizontal and/or vertical) to either be delayed - or 
not activate at all - when placed <0'-4" to nearest wall. My recollection is 
a vacuum condition occurs and there is not sufficient heat build up to 
activate sprinkler. I believe the same phenomenon occurs with smoke detector 
placement. So, 4 to 6 out away from wall (vertical SW) and minimum 4" (to max. 
12"?) down from ceiling/in wall for HSW. The same would apply for placement 
of a pendent sprinkler - if one were needed at 4" from wall...