It's important to keep "Class" 150 or 250 fittings differentiated from Psi
listed or rated. The 300# listing is specific to fire sprinkler piping,
where-as Class refers to a group of fittings for transmission of many
substances including water at various temperatures. For example a (Class
300) S.S. fitting is rated for 720Psi @ 20-100'F but only 450Psi @ 600'F and
365Psi @ 1000'F.
Class includes Pressure ratings, but ref. it to pressure.


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Mike
Cabral
Sent: Tuesday, May 07, 2013 2:18 PM
To: [email protected]
Subject: Re: Listed 400psi weld-o-lets

I would think so however, the safety factor required by UL is different for
various product types. For example a sprinkler head must meet the 4:1 and
plastic pipe 5:1 safety factor. I don't know what the testing calls for
o-lets. 

Sent from my iPhone

On May 7, 2013, at 2:49 PM, "Steve Leyton" <[email protected]>
wrote:

> Concur. My guess is that you could go 4:1 on a groove-o-let up to the 
> same rating as a Vic 75. Ironically, if we can't find a welded 
> solution to satisfy this very particular  AHJ, then we will use 
> grooved saddles which are listed for the same working pressure as the 
> couplings attached to them.
> 
> Steve
> 
> Mike Cabral <[email protected]> wrote:
> 
> I think this is the same issue you experienced when looking for listed 
> high pressure pipe. The 300 psi listing is all the manufacture asked for.
> 
> Sent from my iPhone
> 
> On May 7, 2013, at 2:26 PM, Roland Huggins 
> <[email protected]>
> wrote:
> 
>> Me thinks that is a class rating that does indeed come out of the 
>> steam
> world (like Class 125 being ok for 175 psi water).
>> 
>> Roland
>> 
>> On May 7, 2013, at 11:52 AM, Art Tiroly <[email protected]> wrote:
>> 
>>> Isn't 300 psi a high temp steam rating?
>>> Cold water may be even more than 300 psi.
>>> 
>>> 
>>> Arthur Tiroly
>> 
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.o
> rg
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.o
> rg
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to