It's important to keep "Class" 150 or 250 fittings differentiated from Psi listed or rated. The 300# listing is specific to fire sprinkler piping, where-as Class refers to a group of fittings for transmission of many substances including water at various temperatures. For example a (Class 300) S.S. fitting is rated for 720Psi @ 20-100'F but only 450Psi @ 600'F and 365Psi @ 1000'F. Class includes Pressure ratings, but ref. it to pressure.
-----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Mike Cabral Sent: Tuesday, May 07, 2013 2:18 PM To: [email protected] Subject: Re: Listed 400psi weld-o-lets I would think so however, the safety factor required by UL is different for various product types. For example a sprinkler head must meet the 4:1 and plastic pipe 5:1 safety factor. I don't know what the testing calls for o-lets. Sent from my iPhone On May 7, 2013, at 2:49 PM, "Steve Leyton" <[email protected]> wrote: > Concur. My guess is that you could go 4:1 on a groove-o-let up to the > same rating as a Vic 75. Ironically, if we can't find a welded > solution to satisfy this very particular AHJ, then we will use > grooved saddles which are listed for the same working pressure as the > couplings attached to them. > > Steve > > Mike Cabral <[email protected]> wrote: > > I think this is the same issue you experienced when looking for listed > high pressure pipe. The 300 psi listing is all the manufacture asked for. > > Sent from my iPhone > > On May 7, 2013, at 2:26 PM, Roland Huggins > <[email protected]> > wrote: > >> Me thinks that is a class rating that does indeed come out of the >> steam > world (like Class 125 being ok for 175 psi water). >> >> Roland >> >> On May 7, 2013, at 11:52 AM, Art Tiroly <[email protected]> wrote: >> >>> Isn't 300 psi a high temp steam rating? >>> Cold water may be even more than 300 psi. >>> >>> >>> Arthur Tiroly >> >> _______________________________________________ >> Sprinklerforum mailing list >> [email protected] > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl > er.o > rg > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl > er.o > rg > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl > er.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org