Does the fire pump adding pressure to the system make a difference

On Thu, May 9, 2013 at 10:18 AM, Richard Carr <[email protected]> wrote:

> Greg is correct, and it only applies to pendent heads on drops.
>
> Richard Carr, SET
> Branch Manager
> Cox Fire Protection, Inc
> 6555 Grace Lane.
> Jacksonville, Fl. 32205
> [email protected]
> 904-781-8227
>
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of
> Greg McGahan
> Sent: Thursday, May 09, 2013 10:15 AM
> To: [email protected]
> Subject: Re: Hanger Requirement
>
> Static or Residual pressure...whichever is greater per *9.2.3.4.4.1*
>
>
> On Thu, May 9, 2013 at 9:07 AM, Craig Leadbetter
> <[email protected]>wrote:
>
> > I am working on a building that has a static pressure of 80 PSI and a
> > residual pressure of 50 PSI. The building has a fire pump rated at 750
>
> > gal
> > 70 psi.
> >
> > The questions was raised about the maximum arm over length for
> > sprinklers on the 6th floor of the project that is 93' high to the
> > head location. Do I determine the working pressure from the static or
> > residual pressure when determining if the working pressure is over the
>
> > 100 PSI requirement to require hangers at a maximum of 12"
> >
> > Thanks in advance for any comments
> >
> >
> >
> > --
> > Craig Leadbetter
> > Safeguard of Marquette
> > PO Box 116
> > Marquette, MI 49855
> >
> > (O) 906-475-9955
> > (F) 906-475-5474
> > (C) 906-362-5393
> >
> > [email protected]
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> >
> > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> > er.org
> >
>
>
>
> --
> Greg McGahan
> Living Water Fire Protection, LLC <http://www.livingwaterfp.com>
> 1160 McKenzie Road
> Cantonment, FL 32533
> 850-937-1850
> fax 850-937-1852
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
> .org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>



-- 
Craig Leadbetter
Safeguard of Marquette
PO Box 116
Marquette, MI 49855

(O) 906-475-9955
(F) 906-475-5474
(C) 906-362-5393

[email protected]
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to