Thanks for your replies Matt and Mark

They asked if they needed sprinklers in the racks and I was just checking on
their behalf. I always write up a situation like this as needing a
evaluation as you desiribed and leave it at that,

Chris

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Mark A.
Sornsin, P.E.
Sent: Wednesday, May 29, 2013 9:05 AM
To: [email protected]
Subject: RE: Racks

Chris - there are a couple issues:

1.      This was part of an inspection?  If done per NFPA 25, you would not
be evaluating the adequacy of protection - though as been suggested many
times on this Forum, you may consider a separate note apart from the
inspection forms indicating a concern that there may be an issue. I would
suggest you recommend an evaluation by a qualified engineer. You've
addressed a concern without declaring a position (a task for which you were
not hired).

2.      Ignoring 'why' you were able to see this arrangement, the answer to
your question could very well be, 'yes, they need to add in-rack
sprinklers.'  Let's look at an extreme case: You have a warehouse of metal
parts storage solid piled, with single row racks of expanded plastics to 20
ft. along the exterior walls.  Certainly we can see that OH2 is inadequate
for the plastics so in-racks would be needed (maybe even a higher density at
the ceiling). Your case, while maybe not as stark a contrast in storage,
isn't really different. It all depends on the shelving methods, storage
heights, and the actual commodity classification of the misc. storage in
those racks. But you very well could have a situation where one single-row
rack requires in-racks.

Mark A. Sornsin, P.E. | Karges-Faulconbridge, Inc. | Fire Protection
Engineer | Fargo, ND | direct: 701.552.9905 | mobile: 701.371.5759 |
http://www.kfiengineers.com

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Fire
Protection Services
Sent: Wednesday, May 29, 2013 8:47 AM
To: [email protected]
Cc: [email protected]
Subject: Racks

Forum,



I performed an Inspection a few days ago and the building is design as Ord2
with the exception of the shipping area which is Class 3.

I noticed in a few areas they have installed on single rack against the
outside wall with misc storage stacked at various heights.

I  have never seen one independent rack sprinklered but it looks like to me
it should be.

Has anyone ran into this before? What did you do?



Thanks



Chris Payne

Fire Protection Services

Owensboro



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com
______________________________________________________________________
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to