Brian:

Open rack is defined in 3.9.3.7.7 NFPA 13 ed 2010 , as racks with shelves
with at least 50 % openings.

BR
J.P. Merlino


-----Mensaje original-----
De: [email protected]
[mailto:[email protected]] En nombre de Brian
Harris
Enviado el: jueves, 13 de junio de 2013 04:18 p.m.
Para: [email protected]
Asunto: ESFR & Racks

Quick question for all you storage pro's.... I know that one of the
limitations of using an ESFR system where there is rack storage is that the
shelves cannot be solid.  I don't see anywhere that says what the shelves
can be made out of and is there a percentage of "open" space that the
shelves need to be to not be considered solid?

Brian Harris, CET
BVS Systems Inc.
Sprinkler Division
bvssystemsinc.com<http://bvssystemsinc.com/>
Phone: 704.896.9989
Fax: 704.896.1935

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


-----
No se encontraron virus en este mensaje.
Comprobado por AVG - www.avg.com
Version: 2013.0.2904 / Base de datos de virus: 3199/6404 - Fecha de
publicacion: 06/12/13

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to