Could you flow the line with a 2.5" nozzle and then use the pitot pressure as 
the residual? Somebody call out if I am wrong - but the pitot is usually lower 
than the residual, so you know you would be safe. Then you would have the real 
static, real flow, and a conservatively low "residual". If the flow measures in 
the 1000 gallon range, then you should still have a usable flow number for your 
calculations. The pipes will be a little bigger than if you had the real 
residual pressure, but it could be an option if there is no other way.

Matt Grisé PE*, LEED AP, NICET II  
Sales Engineer 
Alliance Fire Protection 
130 w 9th Ave.
North Kansas City, MO 64116

*Licensed in KS & MO 

913.888.0647 ph 
913.888.0618 f 
913.927.0222 cell 
www. AFPsprink.com 


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Todd - Work
Sent: Wednesday, June 19, 2013 8:15 AM
To: [email protected]
Subject: Re: water test without hydrants

I am looking into hose bibs that are fed from the same main (there is a high 
and low service in that area). 

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
www.fpdc.com

On Jun 19, 2013, at 9:04 AM, Dwight Havens <[email protected]> wrote:

> It is a matter of where you want the test to be "effective".  If you really 
> want to know what the public supply can provide, then thestatic and residual 
> readings need to be taken off of that main.  In Phoenix I used to use the 
> upstream tap on the  nearest backflow prevention assembly, but in Phoenix, 
> these were at the property line, above ground, because we did not worry about 
> freezing conditions.  I have used hose bibs at properties, after ensuring 
> that there were not check valves between the bib and the water supply.
> 
> Regards,
> 
> Dwight
> 
> 
> 
> 
> ________________________________
> From: Todd - Work <[email protected]>
> To: "[email protected]" 
> <[email protected]> 
> Sent: Wednesday, June 19, 2013 8:21 AM
> Subject: Re: water test without hydrants
> 
> 
> Wouldn't that be the equivalent of putting the pressure gauge on another 
> outlet of teh flow hydrant?
> 
> Todd G Williams, PE
> Fire Protection Design/Consulting
> Stonington, CT
> www.fpdc.com
> 
> On Jun 19, 2013, at 8:08 AM, "Martinez, Dewayne" 
> <[email protected]> wrote:
> 
>> Couldn't you just put the pressure gauge on the flange connection before
>> the hose valve?  
>> 
>> -----Original Message-----
>> From: [email protected]
>> [mailto:[email protected]] On Behalf Of
>> Todd - Work
>> Sent: Wednesday, June 19, 2013 6:28 AM
>> To: [email protected]
>> Subject: water test without hydrants
>> 
>> I have a client who tapped a new 6"  line into an 8" public main which
>> does not have any hydrants on it. Now we have to get a flow test. My
>> thought is to put a flange on the 6" with a 2-1/2" hose valve, to which
>> I connect my fire hose and Hose Monster. We would then need to find a
>> nearby property tapped off that line and read pressures from that
>> system. It seems to make sense, but am I missing something?
>> 
>> Todd G Williams, PE
>> Fire Protection Design/Consulting
>> Stonington, CT
>> www.fpdc.com
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
>> .org
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to