If the existing system is designed for ordinary hazard, it's likely the
sprinkler spacing is something greater than 100 sf.  Storage densities at or
greater than .25 gpm/sf require 100 sf max spacing.  Not a deal killer, but
you'd need to discuss it with the AHJ.

Ed Kramer
Lawrence, KS

> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of
> Brian Harris
> Sent: Monday, June 24, 2013 3:04 PM
> To: [email protected]
> Subject: RE: Proposing changes to existing system for new storage
> criteria
> 
> Great point Mark, I never noticed that!
> 
> Brian Harris, CET
> BVS Systems Inc.
> bvssytemsinc.com
> 
> 
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of
> [email protected]
> Sent: Monday, June 24, 2013 4:00 PM
> To: [email protected]
> Subject: RE: Proposing changes to existing system for new storage
> criteria
> 
> I believe Central\Tyco still offers a 1/2" thread 17/32 orifice head.
> That will get you a 30% increase in flow on the same pressure.
> Mark at Aero
> 
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of
> Brian Harris
> Sent: Monday, June 24, 2013 11:06 AM
> To: [email protected]
> Subject: RE: Proposing changes to existing system for new storage
> criteria
> 
> I also considered the possibility of using a higher K factor head at the
> ceiling but all the outlets are 1/2", using mechanical tee's would be
> quite labor intensive. My suggestion of adding Rack Sprinklers seemed
> like the most cost effective way of bringing the current system up to
> code, hence the reason for my post. Just looking for other ideas/
> options, thanks.
> 
> Brian Harris, CET
> BVS Systems Inc.
> bvssytemsinc.com
> 
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of
> [email protected]
> Sent: Monday, June 24, 2013 1:22 PM
> To: [email protected]
> Subject: Re: Proposing changes to existing system for new storage
> criteria
> 
> An adequate sprinkler system is at the core of high-piled combustible
> storage protection. But you, or someone else, needs to start with the
> fire code, and then work towards 13. Someone needs to determine all the
> requirements.
> Inside 13, I'd never automatically say in-rack sprinklers are required.
> I'd go start tracking down what kind of water is available in the main,
> and while that is in progress, go back to commodity classification, see
> what a ceiling only design would require. I'd also talk with business.
> Do they plan on going higher? This is not a project that you can do at
> third hand. It'd be like using a Ouija ( sp ?) Board. Correction from
> down to 15' is considerable. Assuming you can apply Fig. 16.2.1.3.4.1
> design density is reduced 40% in most cases. Can an acceptable design
> density be arrived at by using heads with a higher K-factor? If so, this
> is typically the preferred route.
> It is also easy to forget to consider whether column protection is
> required.
> 
> bv
> 
> ----- Original Message -----
> From: "Brian Harris" < BHarris @ bvssystemsinc .com>
> To: sprinklerforum @lists. firesprinkler .org
> Sent: Monday, June 24, 2013 8:51:54 AM
> Subject: Proposing changes to existing system for new storage criteria
> 
> I got a call the other day form a local company that bought a cold dark
> shell approximately 4 years ago and has been using part of it as a
> storage warehouse for miscellaneous items similar to what you would find
> at any store checkout counter. Lighters, aspirin, pens, various odds and
> ends, and they are stored on racks, mostly in cardboard boxes, with the
> storage as high as 15' in some areas. The other day the AHJ stopped in
> and recommended they cut slats in the wooden shelving to allow the
> overhead system to reach the bottom shelves. At first I thought this
> might work but turns out the overhead system was only designed for AH-2
> using standard 5.6k heads so now it looks like they're gonna definitely
> need rack protection. Any advice or potential problems anyone can see?
> 
> Brian Harris, CET
> BVS Systems Inc.
> Sprinkler Division
> bvssystemsinc .com< http :// bvssystemsinc .com/>
> Phone: 704.896.9989
> Fax: 704.896.1935
> 
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum @lists. firesprinkler .org http ://lists. firesprinkler
> .org/ listinfo . cgi / sprinklerforum - firesprinkler .org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-
> firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-
> firesprinkler.org
> 
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-
> firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-
> firesprinkler.org


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org