All we need is head cover. Thanks to you all
Arthur Tiroly ATCO Fire Protection Design Tiroly and Associates 24400 Highland Rd rm 25, CLE 44143 216-621-8899 216-570-7030 Cell WWW.ATCOfirepro.com -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Thomas Reinhardt Sent: Friday, July 12, 2013 5:23 PM To: [email protected] Subject: RE: Sprinkler dust cover Check out NFPA 25 5.2.1.1. Also the Annex has some suggestions. I believe that cellophane and paper can only be used to protect the head. Wheeling Fire Inspector Tom Reinhardt 2 Community Boulevard Wheeling, IL 60090 847-499-9067 -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Forest Wilson Sent: Friday, July 12, 2013 3:27 PM To: [email protected] Subject: Re: Sprinkler dust cover I dont have a copy of the Standard available; but there is a certain type of plastic which is permitted. The NFSA tested heads with plastic and they didn't work properly. Sent from my iPhone On Jul 12, 2013, at 4:25 PM, Ron Greenman <[email protected]> wrote: > The bags are used to protect the heads from loading as the loaded bags > are cheaper to replace than the heads. Nevertheless, the bags, when > loaded, and once again, a judgement call, need to be replaced. The > bags (paper or 2 mil > plastic) will not interfere with the head opening under a fire condition. > Layers and layers of crap, on the heads or on the bags, will. > > > On Fri, Jul 12, 2013 at 12:19 PM, Art Tiroly <[email protected]>wrote: > >> That section applies to paint booths. Would a bag cover be acceptable >> in a larger open factory building? There are several hundred >> sprinklers involved. >> Old heads are being replaced. Heads are now a dust covered blob. >> >> >> Arthur Tiroly >> ATCO Fire Protection Design >> Tiroly and Associates >> 24400 Highland Rd rm 25, CLE 44143 >> 216-621-8899 >> 216-570-7030 Cell >> WWW.ATCOfirepro.com >> >> -----Original Message----- >> From: [email protected] >> [mailto:[email protected]] On Behalf Of >> Smith, David L.(FAC) >> Sent: Friday, July 12, 2013 2:48 PM >> To: [email protected] >> Subject: RE: Sprinkler dust cover >> >> Art; >> Look at NFPA 13 2010 6.2.6.4.2 also note the annex A >> >> davidsmith >> Fire Suppression Systems Foreman >> Facility Maintenance | City of Lakeland >> 228 S. Massachusetts Ave. Lakeland, Fl. 33801 863/834-2380 (PH) | >> [email protected] www.lakelandgov.net Working together to >> achieve an exceptional quality of life >> >> -----Original Message----- >> From: [email protected] >> [mailto:[email protected]] On Behalf Of >> Art Tiroly >> Sent: Friday, July 12, 2013 2:31 PM >> To: [email protected] >> Subject: RE: Sprinkler dust cover >> >> >> An owner wants us to cover sprinklers with a bag or dust cover to >> keep the sprinklers from becoming loaded with dust. >> >> They say the dust is noncombustible due to chemical additives in the mix. >> >> Is this allowed? >> If not how does he keep them clean? >> >> Arthur Tiroly >> ATCO Fire Protection Design >> 216-621-8899 >> 216-570-7030 Cell >> WWW.ATCOfirepro.com >> >> _______________________________________________ >> Sprinklerforum mailing list >> [email protected] >> >> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprink >> ler.org >> >> ________________________________ >> >> PUBLIC RECORDS NOTICE: >> >> All e-mail sent to and received from the City of Lakeland, Florida, >> including e-mail addresses and content, are subject to the provisions >> of the Florida Public Records Law, Florida Statute Chapter 119, and >> may be subject to disclosure. >> _______________________________________________ >> Sprinklerforum mailing list >> [email protected] >> >> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprink >> ler.org >> >> >> >> ----- >> No virus found in this message. >> Checked by AVG - www.avg.com >> Version: 2012.0.2242 / Virus Database: 3204/5985 - Release Date: >> 07/12/13 >> >> _______________________________________________ >> Sprinklerforum mailing list >> [email protected] >> >> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprink >> ler.org >> > > > > -- > Ron Greenman > Instructor > Fire Protection Engineering Technology Bates Technical College > 1101 So. Yakima Ave. > Tacoma, WA 98405 > > [email protected] > > http://www.bates.ctc.edu/fireprotection/ > > 253.680.7346 > 253.576.9700 (cell) > > Member: > ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC > > They are happy men whose natures sort with their vocations. -Francis > Bacon, essayist, philosopher, and statesman (1561-1626) > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl > er.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org IMPORTANT NOTICE: This e-mail message is intended to be received only by persons entitled to receive the confidential information it may contain. E-mail messages may contain information that is confidential and legally privileged. Please do not read, copy, forward, or store this message unless you are an intended recipient of it. If you have received this message in error, please forward it to the sender and delete it completely from your computer system. _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org ----- No virus found in this message. Checked by AVG - www.avg.com Version: 2012.0.2242 / Virus Database: 3204/5985 - Release Date: 07/12/13 _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org