It would be efficient to start the water supply design by characterizing
the water demand.  Demand should be a reasonable worse-case fire...which
often, but not always, is a full surface burn on white products (probably
kero), but it could be fixed-cone roof tanks of crude at a receiving
terminal.  If crude, you will want more than just big water, because if we
don't lay down in under 4 hours (depending on ullage) we risk our
firefighters' lives to boilover.  Realize tanks with diameters over 200 ft
require foam application rates increased ~20-30% above what NFPA 11
recommends.  The startling truth is, NFPA 11 doesn't have hard
prescriptions for tanks over 200 ft.  But what WE do have -- is real world
experience from the select few firefighters that extinguished these
monsters.

Even if you get the design wrong, odds are a fire in one of the tanks will
not occur for decades on, so your responsibility will be forgotten or
forgiven.  But if a fire in a 200+ ft diameter tank occurs within a handful
of years after completing your work there;  you will be remembered and
looked up.  Costs for incomplete/inaccurate design are in the fraction of
billions when considering: product loss, repair to tank-of-origin and
possibly exposed tanks, repair to hydrant-manifolds, neighboring wetlands,
interruption to neighborhood water supply and normal business practices,
etc.  Then there is the not priceless (just ask BP, since they are still in
business) but the ever costly-- loss of reputation.

Lazlo Czonka sounds Eastern European/Polish.  I know a fire chief at a
Czech terminal who can cover all these topics for you; he has been there
and done this.  Dobre los z tem,

Scot Deal
Excelsior Fire/Risk Engineering