Be careful on your digs.  It was intentionally added to avoid having to size 
the FDC based on system demand in recognition that the FDC will typically slam 
the main supply check closed on typically occupancy hazard facilities  but 
facilities like storage and high rise, it depends (sprinklers only since as 
pointed out standpipes FDC are calc's).  Also if the main supply fails, the 
pumper truck can always juice their supply up further.

Roland


Roland Huggins, PE - VP Engineering
American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves Lives
Dallas, TX
http://www.firesprinkler.org





On Aug 13, 2013, at 8:23 AM, <[email protected]> wrote:

> An FDC "can pump supplemental water" 3.8.1.4 (2013). By definition a 
> supplement is added to something. Not a replacement or a second water supply?
> 
> Sorry I couldn't resist the opportunity to take a dig at the FDC definition 
> in 13.
> 
> Ron F 