Assuming that you do not exceed the psi rating of the components (typically 
175psi) on any given floor, why worry about the pressure at each floor? If you 
do exceed 175psi, the use of a pressure reducing valve at the ground level 
would be a better choice for controlling your pressures. Changing the k-factors 
would only limit your starting head pressures, the pressure available on each 
floor would still remain the same.

Eric Tysinger CET
NICET III - 108988
Project Manager - Fort Myers Branch
Wayne Automatic Fire Sprinklers, Inc.
4683 Laredo Ave.
Fort Myers, Florida 33905
p: (239)433-3030 x1240    f: (239)433-3263
C: (239)633-9703

For Fire Alarm Service and Monitoring questions contact us at:
ftmala...@waynefire.com

"Ask us how we can eliminate your Fire Alarm phone line bills"
"Ask us about CCTV, Access Control and Security"

Thank you, and have a great day !



-----Original Message-----
From: sprinklerforum-boun...@lists.firesprinkler.org 
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Reza 
Esmaeili
Sent: Tuesday, August 13, 2013 3:34 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Different K factor in each floor practical?

Hi!
For a 6 floor business office building considered as light hazard occupancy, 
and the minimum sprinkler discharge density 0.1 gpm/ft2, that the fire pump is 
located in the basement, in order to adjust flow rate of sprinklers not to be 
very high at each floor, what strategy is usually considered? Is it common to 
use different K factor sprinklers in each floor? like the below:
Lets say the pump is 30Gpm at 70Psi and consider the below:
- Pressure at 1st floor= 60 psi ---- I choose a sprinkler with K=2.8 to have 
Q=21.7Gpm
- Pressure at 2nd floor= 50 psi ---- I choose a sprinkler with K=4.2 to have 
Q=29.7Gpm
- Pressure at 3rd floor= 40 psi ---- I choose a sprinkler with K=4.2 to have 
Q=26.7Gpm
- Pressure at 4th floor= 30 psi ---- I choose a sprinkler with K=4.2 to have 
Q=23Gpm
- Pressure at 5th floor= 20 psi ---- I choose a sprinkler with K=5.6 to have 
Q=25Gpm
- Pressure at 6th floor= 10 psi ---- I choose a sprinkler with K=8 to have 
Q=25.3Gpm

The above numbers are theoretical, I just would like to know if it is common to 
change the K factor at each floor to adjust flow rate?
Or may be a pressure regulated valve is better to use at each floor instead of 
different K factor?

Ps. I have considered to use quick response sprinklers.

Thanks!
Reza
www.sarian.ir








________________________________
 From: "bver...@comcast.net" <bver...@comcast.net>
To: sprinklerforum@lists.firesprinkler.org 
Sent: Tuesday, August 13, 2013 5:24 AM
Subject: Re: Sleep on it!
 

Do they stock those foam "dorm" quality mattresses? How many and how stored? 

I think a lot of places don't. If they do, they ignite easy, and burn fast and 
hot. Burn a single one on edge. The fire is essentially over in a minute, with 
just a small residual flame from remnant puddle. 

Temporarily solidified petrochemicals. 

bv 

----- Original Message -----
From: "Charles Thurston" <charl...@mbfsg.com> 
To: "Vince Sabolik" <sprinklerforum@lists.firesprinkler.org> 
Sent: Monday, August 12, 2013 3:07:02 PM 
Subject: Re: Sleep on it! 

Hello Vince, 

Just did one a few months back in a strip center. I will try to remember when I 
get to the office tomorrow and see what it was. 

Monday, August 12, 2013, 5:58:24 PM, you wrote: 

> Hey forum -- 

> Has anyone done a design for a small retail mattress store? 

> Would Class III, Group A really apply? Not really storage... 

> Thanks! 

> Vince Sabolik, West Tech Fire Protection, Inc. 
> 11351 Pearl Road / Strongsville, Ohio 44136 440 
> 238-4800 Fax 440 238-4876 
> ____________________________________________________________________ 


> _______________________________________________ 
> Sprinklerforum mailing list 
> Sprinklerforum@lists.firesprinkler.org 
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org 



-- 
Best regards, 
Charles mailto:charl...@mbfsg.com 

_______________________________________________ 
Sprinklerforum mailing list 
Sprinklerforum@lists.firesprinkler.org 
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org 
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to