FM 7-10 may provide some assistance - deals with woodworking and associated 
timber storage.
I would be interested to know of any other documents dealing specifically with 
cantilever rack solutions.
Luckily they have mostly been timber storage for hardware stores.

Nicky Marshall
Southern Regional Manager
PROTECH DESIGN LIMITED
Specialist Fire Protection Consultants
Phone: 03 579 5577  Mobile: 021 433 488  Email: [email protected]  
Skype: nicky-marshall Web:www.protechdesign.co.nz
Address:105A Alabama Rd, Redwoodtown, Blenheim 7201, NZ Postal:PO Box 4022, 
Redwood Village, Blenheim 7242, NZ

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Cahill, 
Christopher
Sent: Wednesday, 21 August 2013 12:18 PM
To: [email protected]
Subject: Re: Cantilever Racks

I appreciate the thought. Its the design with barriers within the rack and at 
the top. So a little less exposure to the overhead. The deluge activation is 
also about 40' above the top of rack so lesser chance of exposure to overhead. 
And finally future project in next couple years to convert deluge to something 
else making the issue moot. As I said there is a lot to this story.

Chris Cahill
Fire Protection Engineer
Burns & McDonnell
952-656-3652
[email protected] Ed Vining wrote:
Wet blanket thought.  Will FM agree that that interpretation will apply to 
deluge "nozzles" as wel as sprinklers?  In rack sprinklers should reduce the 
number of sprinkler which open, but not the number of deluge nozzles.


On Tue, Aug 20, 2013 at 2:04 PM, Cahill, Christopher
<[email protected]>wrote:

> High piled double row rack storage with in-rack sprinklers.  Per 
> design selected (FM) longitudinal flue heads at every upright and not 
> to exceed 10' o.c.  This is a design that allows one not to consider 
> the overhead sprinklers.  Long story but seemingly the best approach 
> for a reconverted hangar from the 1950's with unknown deluge design.
>
> Cantilever racks with uprights (columns) variable at 2'-8' spacing.  
> Of course the uprights are more like 18" steel columns with 6" 
> flanges.  Does one put a head at every upright? Down to 2' o.c. seems 
> a
little ridiculous?
>  No matter where you put the head there is a large shadow on the other 
> side of the rack/column.  I believe NFPA says locate heads 3" from 
> upright but I think they are talking about the little few inch wide 
> typical rack design not cantilever columns. Thought about solving that 
> problem with a row down each side of the upright but then stuck with 
> the
every upright or 10' o.c.
>  Anyone done a cantilever with in-racks lately?
>
> Chris Cahill, PE*
> Senior Fire Protection Engineer
>
> Ed Vining
4819 John Muir Rd
Martinez CA 94553
925-228-8792
Cell 925-787-0465
*Note the e-mail address change*
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org




_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to