Jeremy,
Refer to NFPA 13, 11.1.6.3.
Size the tank for the sprinkler demand only.
Regards,
G. Tim Stone
G. Tim Stone Consulting, LLC
NICET Level III Engineering Technician
Fire Protection Sprinkler Design
and Consulting Services
117 Old Stage Rd. - Essex Jct., VT. 05452
CELL: (802) 373-0638 TEL: (802) 434-2968 Fax: (802) 434-4343
[email protected]
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of
Jeremy
> Frazier
> Sent: Tuesday, September 03, 2013 10:19 AM
> To: [email protected]
> Subject: Fire Pump with storage tank
>
> When you size a tank, do you size it for 150% of the fire pump demand or
> just the sprinkler demand? Would you also need to include the hose stream
> if there is no inside hose stations? This is the first time I'm doing one
> of these, and I would hate to get this wrong.
>
>
>
>
>
> Jeremy Frazier