If and only if NFPA 45 applies...that's why it is very important for the design 
drawings, preferably the cover sheet or the one immediately behind the cover 
sheet, contain the Code of Record information.  If not available, then the 
engineer (or other qualified design professional) of record needs to establish 
that information, if not already done.  If the design professionals are long 
gone, you may be able to engage the AHJ in determining what applies, since he 
or she is the person that you need to satisfy.

Dwight.




________________________________
 From: Bob <[email protected]>
To: [email protected] 
Sent: Tuesday, September 3, 2013 4:29 PM
Subject: RE: Small Chemical Storage Room
 

Thank you

Bob Knight, CET III
208-318-3057
www.firebyknight.com

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
Johnson, Duane (NIH/OD/ORS) [C]
Sent: Tuesday, September 03, 2013 1:38 PM
To: [email protected]
Subject: RE: Small Chemical Storage Room

NFPA 45 is the standard on laboratories using chemicals. Per NFPA 45:
Educational laboratories can be classified as Class D, fire protection for
Class D is OHI, Class D is permitted to have quantities of flammable liquids
per Table 10.1.1 (a&b) [2011 ed].

See Chapter 10 for more requirements of flammable and combustible liquids.

Duane Johnson, PE
Program Manager
Division of the Fire Marshal (Contractor) Office of Research Services
National Institutes of Health
301-496-0487

"Protecting Science - One Sprinkler at a Time"


-----Original Message-----
From: Bob [mailto:[email protected]]
Sent: Tuesday, September 03, 2013 2:29 PM
To: [email protected]
Subject: Small Chemical Storage Room

I have a project with a small chemical prep/storage room that is 253 sf (19'
x 13'4).  NFPA 13 calls out chemical labs as OH2, but I can't find anything
about the storage/prep.  This is a community college science lab.  What
would be the appropriate design criteria for this room, or what would be the
proper code to reference?

Thanks,

Bob Knight, CET III
208-318-3057




_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to