If there was ever an application of putting a square peg (design spacing) in a 
round hole (actual discharge pattern), sprinklers is it. 

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860-535-2080
www.fpdc.com


On Sep 5, 2013, at 5:31 PM, <[email protected]> wrote:

> Do you mean the same rectangular spray pattern? ( hehe)
> 
> Ron F
> 
> -----Original Message-----
> From: [email protected] 
> [mailto:[email protected]] On Behalf Of Brad 
> Casterline
> Sent: Thursday, September 05, 2013 12:17 PM
> To: [email protected]
> Subject: RE: removing sprinkler on drop
> 
> I still have fresh enough scars to throw SAME PATTERN in there too :)
> 
> -----Original Message-----
> From: Steve Leyton [mailto:[email protected]]
> Sent: Thursday, September 05, 2013 2:06 PM
> To: [email protected]
> Subject: RE: removing sprinkler on drop
> 
> I dunno Pete - didn't we hear a proposal in that regard last week?  Who 
> submitted that?
> 
> The FIRE CODE tells us that, absent a change of use and/or occupancy, a FLS 
> system is required to be maintained in accordance with the code(s) and 
> standard(s) that governed at the time the system and building were
> originally permitted for occupancy.   So you would use your professional
> judgment to select a new sprinkler that most closely approximates the 
> discharge characteristics and RTI of the displaced sprinkler and move
> on.     
> 
> This isn't rocket science.  Is there anyone who thinks that replacing a 
> sprinkler with one of the same K-factor and RTI will compromise the 
> capability of a control-mode system to function properly in that mode?
> Regardless of whether that sprinkler is listed for .03 or .05 or is 
> calculated at .10?
> 
> SML
> 
> 
> 
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Pete 
> Schwab
> Sent: Thursday, September 05, 2013 11:56 AM
> To: [email protected]
> Subject: RE: removing sprinkler on drop
> 
> Steve
> So what do you do if the sprinkler is no longer available? (Residential 
> sprinklers prior to the minimum .05 density and the NFPA 13 2002 requirement 
> for a minimum 0.10 density) Pete
> 
> Peter Schwab
> VP of Purchasing & Engineering Technologies
> 
> Wayne Automatic Fire Sprinklers Inc.
> 222 Capitol Court
> Ocoee, Fl 34761
> 
> Mobile: (407) 468-8248
> Direct: (407) 877-5570
> Fax: (407) 656-8026
> 
> www.waynefire.com
> 
> 
> 
> Celebrating over 34 years of life safety
> 
> 
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Steve 
> Leyton
> Sent: Thursday, September 05, 2013 1:38 PM
> To: [email protected]
> Subject: RE: removing sprinkler on drop
> 
> I didn't mean it as a poke at you - this is the same underlying problem as 
> with ITM.  So long as there are one or two service providers that will do an 
> "inspection" for $250, then it's always going to be that much more 
> challenging to sell a complete and comprehensive professional
> service package into that market.   More universally, the standard
> practice needs to be that sprinklers be replaced when they are removed from 
> fittings, period.  And this will entail hammering on enforcers to hold up 
> their end of the equation as well, which is really the only way
> that unscrupulous corner-cutters can be held accountable.   
> 
> Steve 
> 
> 
> 
> 
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Greg 
> McGahan
> Sent: Thursday, September 05, 2013 10:30 AM
> To: [email protected]
> Subject: Re: removing sprinkler on drop
> 
> "adjust prices"
> With all due respect Steve - I said the WE would comply with code......we are 
> still in the fight every day with those that don't. So issues like this are 
> business killers for those of us that work with the unscrupulous and 
> uneducated....Not that we ourselves are unfallible - but we do at least try.
> 
> 
> On Thu, Sep 5, 2013 at 11:28 AM, Steve Leyton
> <[email protected]>wrote:
> 
>> I was asked about 4 years ago to assist with a lawsuit as either a 
>> technical consultant or designated expert that was focused on this 
>> exact issue.  The case was over a sprinkler that discharged in a
> retail suite
>> that was being remodeled.   A sprinkler contractor had relocated a
>> sprinkler by wrenching out the drop with sprinkler intact, and 
>> reinstalling it a couple feet away.  After they did the work, there 
>> were painters and finishers working in the suite over a weekend.
>> Sunday night, the sprinkler released and flooded the suite, wrecked 
>> the new paint and drywall, etc., etc.
>> 
>> Neither side could prove their points.  The sprinkie alleged that 
>> other trades must have hit the pipe and the finishers and painters 
>> were using pads and rollers on extensions, so that was a distinct
> possibility.
>> And there were teeth marks on the drop, but it wasn't possible to say 
>> forensically and with certainty if they were made during the T.I. or 
>> rough-in.  But, there was no way corroborate the fitter's affidavit
> that
>> he hadn't dropped, wrenched or mishandled the sprinkler.   No forensic
>> conclusions could be reached regarding the sprinkler, as certain parts
> 
>> were missing and someone (a responding firefighter, allegedly) had 
>> badly damaged the sprinkler.  The bottom line is that if the sprinkler
> 
>> had been new, there would have been no allegation of negligence 
>> against the sprinkie.
>> 
>> Whatever sprinklers cost, this is the new price of tea in China folks.
>> Adjust prices and let's move on.
>> 
>> Steve
>> 
>> 
>> 
>> 
>> -----Original Message-----
>> From: [email protected]
>> [mailto:[email protected]] On Behalf Of 
>> Greg McGahan
>> Sent: Thursday, September 05, 2013 9:19 AM
>> To: [email protected]
>> Subject: Re: removing sprinkler on drop
>> 
>> H
>> ave we sufficient evidence that it is the reinstalled heads are the 
>> ones accidently discharging?
>> 
>> It just seems like a waste to throw a 20 dollar head away because you 
>> have to remove and reinstall.....or even a 3 dollar head.
>> 
>> We WILL comply with code, but I strongly disagree.
>> 
>> Greg
>> 
>> 
>> 
>> On Thu, Sep 5, 2013 at 10:54 AM, Todd - Work <[email protected]> wrote:
>> 
>>> I would think that the vast majority of problems in mis-handling 
>>> sprinklers in this manner come from premature actuation (especially 
>>> with glass bulb) and not failure to actuate in a fire. I would also 
>>> think that only in very rare circumstances would you lose a building
> 
>>> due to an accidental discharge of a sprinkler.
>>> 
>>> Todd G Williams, PE
>>> Fire Protection Design/Consulting
>>> Stonington, CT
>>> www.fpdc.com
>>> 
>>> On Sep 5, 2013, at 11:48 AM, "Cahill, Christopher"
>>> <[email protected]>
>>> wrote:
>>> 
>>>> "then it appears you can re-use sprinklers left in drops or
> sprigs"
>>> Where does this appearance come from?  I don't see it in the Code, 
>>> Annex or Handbook.  Quite frankly, that is the only place that 
>>> counts in descending order of priority.
>>>> 
>>>> I agree with Todd there is some judgment and risk tolerance.  I'm 
>>>> sure
>>> not 'buying' a building loss over what a <$10 device I my current
>> role.
>>> When I was a contractor maybe we weren't perfect in this regard.
>>> When I was an AHJ if asked - new, and lot of don't ask don't tell.
>>>> 
>>>> Chris Cahill, PE*
>>>> Senior Fire Protection Engineer
>>>> Burns & McDonnell
>>>> 8201 Norman Center Drive
>>>> Bloomington, MN 55437
>>>> Phone:  952.656.3652
>>>> Fax:  952.229.2923
>>>> [email protected]
>>>> www.burnsmcd.com
>>>> 
>>>> Proud to be one of FORTUNE's 100 Best Companies to Work For 
>>>> *Registered in: MN
>>>> 
>>>> 
>>>> 
>>>> 
>>>> 
>>>> -----Original Message-----
>>>> From: [email protected] [mailto:
>>> [email protected]] On Behalf Of Mark A.
>>> Sornsin, P.E.
>>>> Sent: Thursday, September 05, 2013 10:27 AM
>>>> To: [email protected]
>>>> Subject: RE: removing sprinkler on drop
>>>> 
>>>> I would argue that this shouldn't be an argument as long as it is
>>> specified up-front.  If the owner or engineer says do not reinstall,
> 
>>> then don't argue, because if you win, it is your butt on the line 
>>> should the head fail.
>>>> 
>>>> If this is a competitive bid situation or direct work with owner, 
>>>> with
>>> no c
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>> 
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprin
>>> kl
>>> er.org
>> 
>> 
>> 
>> --
>> Greg McGahan
>> Living Water Fire Protection, LLC <http://www.livingwaterfp.com>
>> 1160 McKenzie Road
>> Cantonment, FL 32533
>> 850-937-1850
>> fax 850-937-1852
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
>> er
>> .org
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> 
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
>> er.org
> 
> 
> 
> --
> Greg McGahan
> Living Water Fire Protection, LLC <http://www.livingwaterfp.com>
> 1160 McKenzie Road
> Cantonment, FL 32533
> 850-937-1850
> fax 850-937-1852
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
> .org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
> .org
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
> .org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> 
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to