I haven't looked it up but will. I believe that previous editions mandated 
schedule #80. That is what we have always done and I believe that it was code 
driven at some point. If I can find it I will post.

Rod at Rapid

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Forest 
Wilson
Sent: Friday, September 06, 2013 9:21 AM
To: [email protected]
Subject: Re: Shoulder Nipple

Schedule 80 is not required or expected. 
The Table in 13: 22.4.3.1.1 contains the info on 1/2" pipe specifically for 
what we are talking about and it is in schedule 40. 

Sent from my iPhone

On Sep 6, 2013, at 10:44 AM, [email protected] wrote:

> Gentlemen"
> 
> 
> As another "old-time" (former) Journeyman Sprinklerfitter (apprentice 
> starting 1974 GRINNELL), we still recognize the conversion of 1/2" upright 
> outlets using Schedule 80 shoulder nipples w/reverse 1/2"x1" 90 "head el" to 
> 1" armover and drop nipple - can't cite 13 requirement, but I always assumed 
> it was to 'beef up' strain on 1/2" nipple with longer armovers...We see them 
> on occasion during our inspections.
> 
> 
> 
> Regards to All/Have a Safe Weekend...
> 
> 
> 
> Jerry**
> 
> 
> [email protected]
> 
> 
> Jerry D. Watts, SFPE
> President & CoFounder
> ACCENT FIRE ENGINEERING INT'L. Ltd.
> Santa Fe/Albuquerque New Mexico
> (800) 503.1961  nationwide
> 
> 
> **New Mexico-Licensed Journeyman Sprinklerfitter #08228
> 
> 
> 
> 
> 
> 
> 
> 
> 
> 
> 
> 
> -----Original Message-----
> From: MPhelps <[email protected]>
> To: sprinklerforum <[email protected]>
> Sent: Fri, Sep 6, 2013 8:33 am
> Subject: Re: Shoulder Nipple
> 
> 
> Has anyone considered the trade off presented with the schedule 80 
> nipple between added structural strength and actual delivered density?  Just 
> thinkin'
> Mark at Aero
> 
> 
> ----- Original Message -----
> From: Charles Thurston [mailto:[email protected]]
> Sent: Friday, September 06, 2013 01:56 PM
> To: [email protected] 
> <[email protected]>
> Subject: Re: Shoulder Nipple
> 
> Hello All,
> 
> For some reason we still have about half a box of 1/2" x Close Sch 80 
> nipples in the warehouse I ordered a while back. I remember seeing 
> that somewhere but can't find it in NFPA 13 2010 or 2013. I know I 
> would not have spent the extra money for them if I did not have to...
> 
> Friday, September 6, 2013, 9:41:27 AM, you wrote:
> 
>> As an "Old Time Fitter" from the early 70's to the 90's before I got 
>> into design, I was taught to use Sch 80 nipples for the additional 
>> strength that they had over the standard Sch 40.
> 
>> On 9/6/2013 5:53 AM, Bobby Gillett wrote:
>>> Duane,
> 
>>> As I mentioned, I was going off of memory. Not sure where exactly the Sch.
> 
>>> 80 came from, maybe it was an old requirement for seismic areas 
>>> before the
> 
>>> limitation of 1" diameter nipples was enforced?? May have been a 
>>> company requirement before that as where I was before was in a 
>>> "seismic zone"...not quite sure. Anybody else out there ever hear of that?
> 
> 
> 
>>> Bobby Gillett
>>> *Living Water Fire Protection, LLC*
>>> 1160 McKenzie Rd.
>>> Cantonment, FL 32533
>>> (850) 937-1850
>>> livingwaterfp.com  <http://livingwaterfp.com/>
> 
> 
>>> On Fri, Sep 6, 2013 at 5:31 AM, Johnson, Duane (NIH/OD/ORS) [C] < 
>>> [email protected]> wrote:
> 
>>>> They are using an existing 1/2" outlet (likely an upright) to 
>>>> supply a relocated sprinkler (likely a pendent)...completely legitimate.
> 
>>>> 8.15.20.4.1 (2013)    When pipe schedule systems are revamped, a nipple
>>>> not exceeding 4 in. (100 mm) in length shall be permitted to be 
>>>> installed in the branch line fitting.
>>>> 8.15.20.4.2    All piping other than the nipple permitted in 8.15.20.4.1
>>>> and 8.15.20.4.3 shall be a minimum of 1 in. (25 mm) in diameter in 
>>>> accordance with Figure 8.15.20.4.2.
>>>> 8.15.20.4.3    When it is necessary to pipe two new ceiling sprinklers
>>>> from an existing outlet in an overhead system, the use of a nipple 
>>>> not exceeding 4 in. (100 mm) in length and of the same pipe thread 
>>>> size as the existing outlet shall be permitted, provided that a 
>>>> hydraulic calculation verifies that the design flow rate will be 
>>>> achieved in accordance with Figure 8.15.20.4.3.
>>>> 8.15.20.4.4    Where an armover is attached to connect to a sprinkler, the
>>>> use of pipe nipples less than 1 in. (25 mm) in diameter shall not 
>>>> be permitted where seismic design is required on the system.
> 
>>>> By the way, where did the sch 80 requirement come from? I have 
>>>> never been able to locate that in code.
> 
>>>> Duane Johnson, PE
>>>> Program Manager
>>>> Division of the Fire Marshal (Contractor) Office of Research 
>>>> Services National Institutes of Health
>>>> 301-496-0487
> 
>>>> "Protecting Science - One Sprinkler at a Time"
> 
> 
>>>> -----Original Message-----
>>>> From: Bobby Gillett [mailto:[email protected]]
>>>> Sent: Thursday, September 05, 2013 10:46 PM
>>>> To: [email protected]
>>>> Subject: Re: Shoulder Nipple
> 
>>>> Hoping they are requesting sch 80 and they are not in a seismic zone.
> 
>>>> Sent from my iPhone
> 
>>>> On Sep 5, 2013, at 9:12 PM, "JSM Fire Pro" <[email protected]> wrote:
> 
>>>>> You’re a third party glancing over a bill of materials for an 
>>>>> add/relocate day job.  You notice one of the line items is calling 
>>>>> for
>>>> several ½”
>>>>> shoulder nipples.
> 
> 
> 
>>>>> What goes through your mind?
> 
> 
> 
>>>>> J. Scott Mitchell, PE
> 
>>>>> B&W Technical Services Pantex
> 
>>>>> _______________________________________________
>>>>> Sprinklerforum mailing list
>>>>> [email protected]
>>>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firespr
>>>>> inkl
>>>>> er.org
>>>> _______________________________________________
>>>> Sprinklerforum mailing list
>>>> [email protected]
> 
>>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firespri
>>>> nkler.org _______________________________________________
>>>> Sprinklerforum mailing list
>>>> [email protected]
> 
>>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firespri
>>>> nkler.org
> 
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprin
>>> kler.org
> 
> 
>>> -----
>>> No virus found in this message.
>>> Checked by AVG - www.avg.com
>>> Version: 2013.0.3392 / Virus Database: 3222/6641 - Release Date: 
>>> 09/05/13
> 
> 
> 
> 
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprink
>> ler.org
> 
> 
> 
> --
> Best regards,
> Charles                            mailto:[email protected]
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org
> 
> 
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org
_______________________________________________