Ampeck,

The European distributors of Viking, Tyco, Victaulic etcetera can supply you off the shelve with FM approved OS&Y valves, drilled with PN16 bolt circles.
Drilling it yourselves voids the listing.

Is this a horizontal split case pump?
If so, can't you install the OS&Y valve on the upstream side of the piece of suction pipe mentioned in NFPA 20 (2013) par. 4.14.6.3.2 ? Doing so will allow you to connect that suction pipe with a DIN PN16 flange to the pump and with an ASA flange to the OS&Y valve.

On the discharge side you usually won't have an OS&Y valve directly connected to the pump.
See NFPA 20 (2013) Figure A.4.30(a) and the diagrams in the Appendix.

Best regards,

Frans Stoop
TOS architecture & fire protection
Netherlands <[email protected]>
Tel. +31-24-324 0112


At 16:45 6-9-2013 +0500, you wrote:
This is not quite sprinkler related but it's dealing with a fire pump and metric versus imperial units.

I have a pump installed by a Turkish contractor. We're revamping the pump piping to conform as good as we can to NFPA.

Well we tried to bolt our OS&Y valve up to their pump and the bolt circle is a little smaller then ours. Our valves as all from the USA and that's what the client wants. So now I'm faced with boring out the holes or something to make them match up.

The flange has a PN16 which is less than a 150 class flange, which would be roughly PN20. Besides machine drilling the holes, anyone run into this before? We have groove flange adapters that will accommodate the PN16 flange. Just means we'll have to add in a little piece of pipe and order more groove flange adapters from the states.

Thanks!
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


-----
Geen virus gevonden in dit bericht.
Gecontroleerd door AVG - www.avg.com
Versie: 2013.0.3392 / Virusdatabase: 3222/6642 - datum van uitgifte: 09/06/13

------------------disclaimer------------------
Senders and recipients of e-mail should be aware that there is no such thing as a confidential e-mail. On its way between sender and recipient each e-mail message is stored and transfered by numerous servers, each of which can be located anywhere in the world. Some servers keep your e-mail correspondence on storage for a short time only, other servers may store the communication for many years. In some countries the authorities filter all e-mail correspondence passing by and may decide to read your content. Also, many operators of the e-mail servers can easily read your messages. ------------------disclaimer------------------
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to