Jimmy,

I would guess that if your pump discharge PSI at the 150% rated GPM test
flow (from the pump curve) is higher that what you calculated for the
required pump discharge, you have proved it-- (demand is 'under the curve'
using that pipe size).

-----Original Message-----
From: James D. Waite [mailto:[email protected]] 
Sent: Wednesday, September 18, 2013 6:10 PM
To: [email protected]
Subject: Fire Pump Test Header Calculation

Can I get some assistance with a fire pump test header calculation?

I got the calculation form from 20:4.20.3.4, and I have it filled out.  But
what to I do next?  How do I use it to confirm the pipe size?


Jimmy Waite, CET - Design Manager
Fire & Life Safety America- Raleigh District
7711 Welborn Street, Suite 103
Raleigh, NC  27615
Office: 919-872-3250
Cell: 919-868-3546
Fax: 919-877-5775
www.flsamerica.com<https://owa.flsamerica.com/owa/www.flsamerica.com>


________________________________

The information contained in this email and any attached documents may
contain information that is the confidential property of Fire & Life Safety
America, Inc ("FLSA"). Any documents created on any FLSA computer or by any
employee in the conduct of FLSA business is work product and owned by FLSA.
If the reader of this message is not the intended recipient, or the employee
or agent responsible to deliver it to the intended recipient, you are hereby
notified that any dissemination, distribution or other use of the contents
of this communication is strictly prohibited. If you have this communication
in error, please immediately notify the sender and delete this email.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to