IFC - 903.2.11.4 Ducts conveying hazardous exhausts.

IMC - 510.7 Suppression required.
Ducts shall be protected with an approved automatic fire suppression system 
installed in accordance with the International Building Code.

[F] 510.2.1 Lumber yards and woodworking facilities.
Equipment or machinery located inside buildings at lumber yards and woodworking 
facilities which generates or emits combustible dust shall be provided with an 
approved dust-collection and exhaust system installed in conformance with this 
section and the International Fire Code. Equipment and systems that are used to 
collect, process or convey combustible dusts shall be provided with an approved 
explosion-control system.

There are several interpretations out there of what to actually do - sprinklers 
(IMC 510.7), sprinkler and explosion venting(IMC 510.7 and 510.2.1), spark 
suppression systems (IMC 510.2.1)....

Chris Cahill, PE*
Senior Fire Protection Engineer 
Burns & McDonnell
8201 Norman Center Drive
Bloomington, MN 55437
Phone:  952.656.3652
Fax:  952.229.2923
[email protected]
www.burnsmcd.com

Proud to be one of FORTUNE's 100 Best Companies to Work For
*Registered in: MN





-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Steve 
Leyton
Sent: Thursday, September 19, 2013 11:33 AM
To: [email protected]
Subject: Dust collection - where/when are sprinklers required

I have looked through the California editions of International Fire Code and 
Building Code and cannot find any prescriptives for sprinklers in
dust collection systems in woodworking facilities.   Does anyone know
where the triggers are published, if anywhere?  Is it in NFPA 664?

 

Steve Leyton

PROTECTION DESIGN & CONSULTING

2851 Camino del Rio South, Suite 400

San Diego, CA 92108

-------------------------------------------------------------

Ph:      858.751.2930 - ext. 102

Fax:    858.751.2933

Cell:  619.972.5696

 

 

 

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to