Maybe the push to change was to stop any K-Factor War between manufacturers.
I have heard it said there was an RTI war and that is why the makers stopped
publishing the RTI in the data, i.e., "this head activates the square root
of X feet-seconds faster than this one so it has to be better". But with
K-factors it is more noticeable because the numbers in the calc sheets are
all 2 or 3 decimal places "accurate", so why shouldn't K be?

-----Original Message-----
From: Roland Huggins [mailto:[email protected]] 
Sent: Tuesday, September 24, 2013 4:50 PM
To: [email protected]
Subject: Re: old 14.5k ecoh brass upright

I think it was the 99 edition when it was changed so it has been awhile.


Roland Huggins, PE - VP Engineering
American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves Lives
Dallas, TX
http://www.firesprinkler.org





On Sep 24, 2013, at 1:11 PM, Brad Casterline <[email protected]>
wrote:

> ya ok thanks John, and Roland I was just looking at that section, thanks.
I
> guess the manufacturer publishes the nominal K-factor in their data, even
> though I have not seen it called that. It has been quite a while since I
> have used 5.62 or 8.2 instead of 5.6 and 8.0, and it seems this change
from
> specific to nominal is the reason!