It's also defined, well sort of in the Annex, in '13 A8.6.5.2.1.4.  ... If an 
obstruction is so close to a sprinkler that water cannot spray on both sides, 
it is effectively a continuous obstruction as far as the sprinkler is concerned 
and the Beam Rule should be applied....this has been around for many editions. 
I'd also point out the section 8.6.5.2 applies to both continuous and 
non-continuous obstructions thus why the point in the annex becomes relevant.  
I have seen folks use the 3 times rule to argue there are allowable shadow 
areas and translate that to whatever situation they are dealing with.  IOW when 
is a head so close to a sprinkler that water cannot spray on both sides, well 
when it affects more than the allowable floor area already allowed by the 3 
times rule.  

And it is different than the new definition 3.3.18.1 Continuous Obstruction. An 
obstruction located at or below the level of sprinkler deflectors that affect 
the discharge pattern of two or more adjacent sprinklers.

Is effectively continuous the same continuous?  

So, it is an obstruction that affects at least two sprinklers or at least one 
sprinkler.  Seems rather clear to me, lol. 

Chris Cahill, PE*
Senior Fire Protection Engineer 
Burns & McDonnell
8201 Norman Center Drive
Bloomington, MN 55437
Phone:  952.656.3652
Fax:  952.229.2923
[email protected]
www.burnsmcd.com

Proud to be one of FORTUNE's 100 Best Companies to Work For
*Registered in: MN




-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of 
[email protected]
Sent: Tuesday, October 01, 2013 3:05 PM
To: [email protected]
Subject: Re: Continuous Obstruction

It is defined.  See 3.3 18.  in the 2013 edition.

John Hoffman P.E. | Fire Protection Engineer | Facility Engineering Services, 
KCP, LLC - Burns & McDonnell Engineering | National Nuclear Security 
Administration's Kansas City Plant | Operated by Honeywell FM&T |
2000 E. 95th St | Kansas City, MO  64131 | ph 816-997-7213 | [email protected]



From:   "G. Tim Stone" <[email protected]>
To:     <[email protected]>
Date:   10/01/2013 02:58 PM
Subject:        Continuous Obstruction
Sent by:        [email protected]



Can someone please provide me a definition for the term "Continuous 
Obstruction" as referenced in NFPA 13, 13D or 13R.

I wonder why this is not defined in NFPA 13, Chapter 3.

Are round semispherical surface mounted light fixtures (found in residential 
dwelling units) considered such? 

 

Thank you in advance.

 

 

Regards,

G. Tim Stone

 

G. Tim Stone Consulting, LLC

NICET Level III Engineering Technician

Fire Protection Sprinkler Design

and Consulting Services

 

                117 Old Stage Rd. - Essex Jct., VT. 05452

CELL: (802) 373-0638   TEL: (802) 434-2968   Fax: (802) 434-4343

                            <mailto:[email protected]> [email protected]

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to