903.3.1.1.1 Exempt locations.
Automatic sprinklers shall not be required in the following rooms or areas 
where such rooms or areas are protected with an approved automatic fire 
detection system in accordance with Section 907.2 that will respond to visible 
or invisible particles of combustion. Sprinklers shall not be omitted from any 
room merely because it is damp, of fire-resistance-rated construction or 
contains electrical equipment. 

    1. Any room where the application of water, or flame and water, constitutes 
a serious life or fire hazard. 

    2. Any room or space where sprinklers are considered undesirable because of 
the nature of the contents, when approved by the fire code official. 

    3. Generator and transformer rooms separated from the remainder of the 
building by walls and floor/ceiling or roof/ceiling assemblies having a 
fire-resistance rating of not less than 2 hours. 

    4. Rooms or areas that are of noncombustible construction with wholly 
noncombustible contents. 

    5. Fire service access elevator machine rooms and machinery spaces. 

    6. Machine rooms and machinery spaces associated with occupant evacuation 
elevators designed in accordance with Section 3008. 


Duane Johnson, PE
Program Manager
Division of the Fire Marshal (Contractor)
Office of Research Services 
National Institutes of Health 
301-496-0487

"Protecting Science - One Sprinkler at a Time"


-----Original Message-----
From: John Drucker - Home [mailto:[email protected]] 
Sent: Tuesday, October 15, 2013 11:02 PM
To: [email protected]
Subject: RE: 2012 IBC Sprinkler Prohibition

Jack, all the code references,

In order, 
1) When Required, Fire Service and Occupant Evac
2) Sprinkler Prohibitions
3) Machine Room protection



403.5.2 Additional exit stairway. For buildings other
than Group R-2 that are more than 420 feet (128 000 mm)
in building height, one additional exit stairway meeting
the requirements of Sections 1009 and 1022 shall be provided
in addition to the minimum number of exits required
by Section 1021.1. The total width of any combination of
remaining exit stairways with one exit stairway removed
shall be not less than the total width required by Section
1005.1. Scissor stairs shall not be considered the additional
exit stairway required by this section.

Exception: An additional exit stairway shall not be
required to be installed in buildings having elevators
used for occupant self-evacuation in accordance with
Section 3008.

403.6.1 Fire service access elevator. In buildings with an
occupied floor more than 120 feet (36 576 mm) above the
lowest level of fire department vehicle access, no fewer
than two fire service access elevators, or all elevators,
whichever is less, shall be provided in accordance with
Section 3007. Each fire service access elevator shall have
a capacity of not less than 3500 pounds (1588 kg).

403.6.2 Occupant evacuation elevators. Where installed
in accordance with Section 3008, passenger elevators for
general public use shall be permitted to be used for occupant
self-evacuation.



SECTION 3007
FIRE SERVICE ACCESS ELEVATOR
3007.1 General. Where required by Section 403.6.1, every
floor of the building shall be served by fire service access elevators
complying with Sections 3007.1 through 3007.10.
Except as modified in this section, fire service access elevators
shall be installed in accordance with this chapter and
ASME A17.1/CSA B44.

3007.3.1 Prohibited locations. Automatic sprinklers shall
not be installed in elevator machine rooms, elevator
machine spaces, and elevator hoistways of fire service
access elevators.

SECTION 3008
OCCUPANT EVACUATION ELEVATORS
3008.1 General. Where elevators are to be used for occupant
self-evacuation during fires, all passenger elevators for general
public use shall comply with Sections 3008.1 through
3008.11. Where other elevators are used for occupant selfevacuation,
they shall also comply with these sections.

3008.3.1 Prohibited locations. Automatic sprinklers shall
not be installed in elevator machine rooms and elevator
machine spaces for occupant evacuation elevators.

3006.4 Machine rooms and machinery spaces. Elevator
machine rooms and machinery spaces shall be enclosed with
fire barriers constructed in accordance with Section 707 or
horizontal assemblies constructed in accordance with Section
711, or both. The fire-resistance rating shall be not less than
the required rating of the hoistway enclosure served by the
machinery.

Hope that helps,


John Drucker, CET
Fire Protection Subcode Official
Fire / Building / Electrical Inspector
New Jersey





-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
Fairchild, Jack
Sent: Tuesday, October 15, 2013 10:46 AM
To: [email protected]
Subject: RE: 2012 IBC Sprinkler Prohibition

Thanks John,

A cursory read of the section produced a visceral response.  After a little
thought, I see where they are going and am not sure they went far enough.
If suppression is to be removed from the machine room, the machine room
should be in an easily accessible location and should be protected with a
rating equivalent to the shaft without exception.
  

Jack Fairchild

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of John
Drucker
Sent: Tuesday, October 15, 2013 10:35 AM
To: [email protected]
Subject: Re: 2012 IBC Sprinkler Prohibition

Jack. I'm on the road so don't have code in front, check also chapter 10
means of egress occupant evac and fire service elevators, there are similar
prohibitions. 
John Drucker - Mobile Email

----- Original Message -----
From: [email protected]
<[email protected]>
To: [email protected]
<[email protected]>
Sent: Tue Oct 15 10:32:08 2013
Subject: 2012 IBC Sprinkler Prohibition

Reference: 2012 IBC 3007.3.1.  Is this the only section of the IBC where
sprinkler are specifically prohibited from a location?  Why would they do
this?  In my mind this just stirs the pot of the ol' sprinkler vs. elevator
argument.

Jack Fairchild


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


CONFIDENTIAL AND PROPRIETARY:
This email message is intended only for the use of the individual or entity
to which it is addressed and may contain information that is privileged and
confidential, nor is it, unless specifically stated, intended to be relied
upon by any person or persons other than the individual or entity named
above and no warranties or representations are made or intended to persons
or entities not named above.  If the reader is not the intended recipient,
you are hereby notified that any dissemination, distribution or copying of
this communication is strictly prohibited.  If you have received this
communication in error, please notify us immediately by telephone, return
this message to the address above and delete all copies.  Thank you.

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to