As long as you are in Chapter 13, Chapter 11 modifiers apply as applicable.

John

It should be recognized that the above is my opinion as a member of the NFPA 13 
Technical Committee on Sprinkler Discharge Criteria, and has not been processed 
as a formal interpretation in accordance with the NFPA Regulations Governing 
Committee Projects and should therefore not be considered, nor relied upon, as 
the official position of the AFSA nor the NFPA, nor any of their technical 
committees.

John August Denhardt, P.E., FSFPE
Strickland Fire Protection Incorporated
5113 Berwyn Road
College Park, Maryland 20740
Office Telephone Number:  301-474-1136
Mobile Telephone Number:  301-343-1457
FIRE SPRINKLERS SAVE LIVES - Can you live without them?


-----Original Message-----
From: sprinklerforum-boun...@lists.firesprinkler.org 
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Ed Kramer
Sent: Wednesday, November 20, 2013 10:15 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Misc storage and QR sprinkler deduction

Todd, take a peek at 13.2.2 (2)   (2013 edition).

Ed Kramer
Lawrence, KS

-----Original Message-----
From: sprinklerforum-boun...@lists.firesprinkler.org
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Todd -
Work
Sent: Wednesday, November 20, 2013 8:45 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Misc storage and QR sprinkler deduction

I am working on a school project where there is a basement that will be used
for storage (3300 sqft, 13 ft ceiling). I am basing my design on 10 ft high
storage of miscellaneous stuff, which I am calling Class IV. This would be a
0.20/1500 sprinkler density, which is the same as the requirement for OH2.
Since I have a marginal water supply and am at the far end of the system,
minimizing the design is critical. 

My question is this; can I use the RA deduction for QR heads in OH2 with the
curves for low piled storage? Or does the fact that this is storage negate
that reduction?

Must be my day for question....



Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
www.fpdc.com
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to