You say flawed air supply.  I hear moisture getting into system from relatively 
moist air coming from the warm space and condensing and freezing at the -20 
interface point. This isn't a low point problem from hydro testing or a place 
where you have a freeze thaw cycle which would allow water to move about.  You 
can't get water (humidity, moisture) much past the interface point.  The air 
coming from the compressor has a dew point, certainly much higher than -20.  As 
soon as the air reaches the dew point is condenses out and if below 32 turns to 
ice.  Once it's ice it's done moving. This all happens right around the 
interface.  The pipe/air a few feet on the warm side is above 32 and it remains 
water.  The only way to get ice remote from this point I think is to move it 
fast so it cools below its dew point farther along the path.  Air ain't moving 
fast in a dry (PA, DIPA) system.  And even then you'd get a gradient of ice not 
a pocket someplace else.  I'd love to hear other thoughts on how it's possible 
to get ice remote where the moisture is from a compressor drawing in warm air. 
I don't think it's possible.   

I also defer to you looking at it.  And seeing what I'm not.  Your reality 
could be different than my idealized thoughts.  

Chris Cahill, PE*
Senior Fire Protection Engineer 
Burns & McDonnell
8201 Norman Center Drive
Bloomington, MN 55437
Phone:  952.656.3652
Fax:  952.229.2923
[email protected]
www.burnsmcd.com

Proud to be one of FORTUNE's 100 Best Companies to Work For
*Registered in: MN





-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Steve 
Leyton
Sent: Monday, December 02, 2013 6:20 PM
To: [email protected]
Subject: RE: Ice plug detection

Chris:

We know exactly where the principal plugs are and why.  I am programming a 
remediation and upgrade to address the cause, which is flawed air supply design 
and installation.  The client raised the issue today of assessing the entire 
installation and assuring it's free of all plugs that may have formed 
downstream of where the recurring problem is located.  Work area is very cold, 
frozen food storage, can't introduce stuff that will dirty the air, booger up 
the environment, etc.  

Anyone know for sure if ultrasound equipment will work in -20°F?

Steve  




-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Cahill, 
Christopher
Sent: Monday, December 02, 2013 3:20 PM
To: [email protected]
Subject: RE: Ice plug detection

Why do you think you have plugs? Attic system or freezer?  

They usually form at the transition from warm to cold.  Should be within a few 
feet of that on the cold side.   And I'm sure per NFPA 13, pick your edition, 
been there a very long time.  
7.9.2* Spaces Maintained at Temperatures Below 32°F (0°C).
7.9.2.1 General.
7.9.2.1.1 Where sprinkler pipe passes through a wall or floor into the 
refrigerated space, a section of pipe arranged for removal shall be provided 
immediately inside the space.
7.9.2.1.2 The removable length of pipe required in 7.9.2.1.1shall be a minimum 
of 30 in. (762 mm).  

Chris Cahill, PE*
Senior Fire Protection Engineer
Burns & McDonnell
8201 Norman Center Drive
Bloomington, MN 55437
Phone:  952.656.3652
Fax:  952.229.2923
[email protected]
www.burnsmcd.com

Proud to be one of FORTUNE's 100 Best Companies to Work For *Registered in: MN





-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Steve 
Leyton
Sent: Monday, December 02, 2013 5:13 PM
To: [email protected]
Subject: Ice plug detection

Okay, slow day, I'll go first.   So ... who's got suggestions about how
to find ice plugs in existing systems without pulling everything apart or 
running a borescope down the piping?

 

Steve Leyton

PROTECTION DESIGN & CONSULTING

2851 Camino del Rio South, Suite 400

San Diego, CA 92108

-------------------------------------------------------------

Ph:      858.751.2930 - ext. 102

Fax:    858.751.2933

Cell:  619.972.5696

 

 

 

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to