Steve,
Is there a section you can point me to?

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
Steven Scandaliato
Sent: Tuesday, January 07, 2014 10:30 AM
To: [email protected]
Subject: RE: Plastic rack storage

If the adjacent rack(s) are at least 4ft away then no.

Steven Scandaliato, SET CFPS
520.971.2322 Cell
Skype: steven.scandaliato


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
Martinez, Dewayne
Sent: Tuesday, January 07, 2014 10:14 AM
To: [email protected]
Subject: Plastic rack storage

NFPA 13 (07ed) section 17.2.4.3 (2)

 

This section requires me to calculate 14 sprinklers (7 on top two
levels).
I have a situation where my racks are not long and would only have 4
heads on the top two levels.  I don't see a section like
16.2.4.3.2 that allows me to stop with only one rack.  Would I have to
pick up the remaining sprinklers in the next adjacent rack?

Thanks,

 

Dewayne