In reviewing my own questions, I see in NFPA 13 Chapter 16 2013 that class I - 
IV storage to 25' high with a 35' deck K14 are still shown @ 75-psi.  Over 40' 
deck with 25' storage they are not shown.  However, for storage of class I - IV 
greater than 25',  a building with a 40' deck and 30' storage they are shown at 
75-psi.  So it looks like there is an issue with the clearance between top of 
storage and deck  that is going to dictate when K14's are allowed.  I have not 
checked the other storage chapters yet, but I will.  Any one's input still 
would be interesting.    

Thanks,
Gregg Fontes
Cen-Cal Fire Systems, Inc.
209-334-9119
-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Gregg 
Fontes
Sent: Tuesday, January 14, 2014 2:22 PM
To: [email protected]
Subject: ESFR K14 Sprinklers

The following was sent to me by a developer.  I had heard some rumors through 
the circles that this may be happening.  Has any seen or heard that this is 
truly happen later this year?

We're finding out (via a tenant's fire consultant) that the fire code changes 
in September 2014 in that they no longer allow K14 sprinkler heads in new 
construction. Also, only a certain (newer)  type of the K17 head which only two 
manufacturers have in limited supply but are production. 
We're finding that many fire jurisdictions and contractors are not yet aware 
and have not commented back to us.

Thanks,
Gregg Fontes
Cen-Cal Fire Systems, Inc.
209-334-9119

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to