I don't believe the "letter of the law" requires it be fed off the top of the 
line, there is a figure that has a note that says it is, but that figure is a 
part of the Annex, and thusly not enforceable?  Also the reason stated in the 
note is moot when you also provide a drum drip (condensation).

Mike Morey, CFPS, SET
Planner Scheduler/Designer
BMWC Constructors, Inc.
1740 W. Michigan St, Indianapolis, IN 46222
O: 317.651.0596 | C: 317.586.8111
[email protected] | www.bmwc.com

________________________________________
From: [email protected] 
[[email protected]] on behalf of Scott A Futrell 
[[email protected]]
Sent: Thursday, January 23, 2014 11:48 AM
To: [email protected]
Subject: RE: Dry System I.T.C.

How do you do that when 13 requires the drain off the bottom of the pipe and 
the inspectors test off the top of the highest most remote sprinkler?

Scott Futrell

(763) 425-1001 x12 Office
(612) 759-5556 Cell


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of John 
Denhardt
Sent: Thursday, January 23, 2014 10:42 AM
To: [email protected]
Subject: RE: Dry System I.T.C.

Same here - All the time.

John August Denhardt, P.E., FSFPE
Strickland Fire Protection Incorporated
5113 Berwyn Road
College Park, Maryland 20740
Office Telephone Number:  301-474-1136
Mobile Telephone Number:  301-343-1457
FIRE SPRINKLERS SAVE LIVES - Can you live without them?


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Vince
Sent: Thursday, January 23, 2014 11:43 AM
To: [email protected]
Subject: RE: Dry System I.T.C.

All the time.

-------- Original message --------
From: Brian Harris <[email protected]>
Date:01/23/2014  11:39 AM  (GMT-05:00)
To: [email protected]
Subject: Dry System I.T.C.

Has anyone ever used a Drum Drip (aux. drain) on a dry system as the I.T.C. as 
well ?

Brian Harris, CET
BVS Systems Inc.
Sprinkler Division
bvssystemsinc.com<http://bvssystemsinc.com/>
Phone: 704.896.9989
Fax: 704.896.1935

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to