And the FDC reference pointing to 312;

2009 IFC SECTION 912 - FIRE DEPARTMENT CONNECTIONS


912.3.3 Physical protection. Where fire department connections
are subject to impact by a motor vehicle, vehicle
impact protection shall be provided in accordance with Section
312.


John Drucker, CET
Assistant Construction Official
Fire Protection Subcode Official
Building/Fire/Electrical Inspector
Borough of Red Bank
Red Bank, New Jersey
Email: [email protected]
Cell/Text: 732-904-6823


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of John
Drucker - Home
Sent: Saturday, February 8, 2014 8:21 PM
To: [email protected]; [email protected]
Subject: RE: Bollard Diameter

2009 IFC

312.1 General. Vehicle impact protection required by this code shall be
provided by posts that comply with Section 312.2 or by other approved
physical barriers that comply with Section 312.3.

312.2 Posts. Guard posts shall comply with all of the following
requirements:
1. Constructed of steel not less than 4 inches (102 mm) in diameter and
concrete filled.
2. Spaced not more than 4 feet (1219 mm) between posts on center.
3. Set not less than 3 feet (914 mm) deep in a concrete footing of not less
than a 15-inch (381 mm) diameter.
4. Set with the top of the posts not less than 3 feet (914 mm) above ground.
5. Located not less than 3 feet (914 mm) from the protected object.

312.3 Other barriers. Physical barriers shall be a minimum of
36 inches (914 mm) in height and shall resist a force of 12,000 pounds (53
375 N) applied 36 inches (914 mm) above the adjacent ground surface.

Hope that helps,


John Drucker, CET
Assistant Construction Official
Fire Protection Subcode Official
Building/Fire/Electrical Inspector
Borough of Red Bank
Red Bank, New Jersey
Email: [email protected]
Cell/Text: 732-904-6823


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Owen
Evans
Sent: Saturday, February 8, 2014 7:32 PM
To: [email protected]
Subject: Bollard Diameter

Hello Folks,


The minimum diameter of a bollard protecting an FDC is 4" correct? Can
someone give me the code reference? 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to