Correct. But only the fittings are black, the pipe is galvanized.

Jimmy Waite, CET - Design Manager
Fire & Life Safety America- Raleigh District
7711 Welborn Street, Suite 103
Raleigh, NC  27615
Office: 919-872-3250
Cell: 919-868-3546
Fax: 919-877-5775
www.flsamerica.com




-----Original Message-----
From: sprinklerforum-boun...@lists.firesprinkler.org 
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Mike 
Hairfield
Sent: Friday, February 14, 2014 9:46 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Dry System with Galvanized Pipe and Black Fittings

You have never been able to use a C factor of 120 for black steel pipe on a dry 
system.


> From: jdwa...@flsamerica.com
> To: sprinklerforum@lists.firesprinkler.org
> Subject: RE: Dry System with Galvanized Pipe and Black Fittings
> Date: Fri, 14 Feb 2014 14:42:01 +0000
>
> What I was looking for (and thought I'd seen before) was that even if I used 
> black steel fitting on galvanized pipe I could still calculate the system 
> using a C factor of 120. I thought I remembered seeing it way back in 2002, 
> and was trying to trace it forward.
>
> Jimmy Waite, CET - Design Manager
> Fire & Life Safety America- Raleigh District
> 7711 Welborn Street, Suite 103
> Raleigh, NC 27615
> Office: 919-872-3250
> Cell: 919-868-3546
> Fax: 919-877-5775
> www.flsamerica.com
>
>
>
> -----Original Message-----
> From: sprinklerforum-boun...@lists.firesprinkler.org
> [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of
> Steve Mackinnon
> Sent: Friday, February 14, 2014 9:35 AM
> To: sprinklerforum@lists.firesprinkler.org
> Subject: RE: Dry System with Galvanized Pipe and Black Fittings
>
> For dry and double interlocked pre action systems, black pipe is c of 100. 
> Galv is c of 120.
> For wet and single interlocked pre action systems, all steel piping is 120.
>
> Steven MacKinnon
> Fire Protection Division
> Hartcorn Plumbing and Heating, Inc.
> 850 South Second Street
> Ronkonkoma, NY 11779
> Office 631-580-2300 Fax - 631-580-1090
>
>
> -----Original Message-----
> From: sprinklerforum-boun...@lists.firesprinkler.org
> [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of
> Aaron Peck
> Sent: Friday, February 14, 2014 9:32 AM
> To: sprinklerforum@lists.firesprinkler.org
> Subject: Re: Dry System with Galvanized Pipe and Black Fittings
>
> I got the 2010, 13 code on my iPhone but I'm still useless trying to find 
> anything. Give me the book and I can turn right too it. Go figure.
>
> It may have been 100 before, did they change it in 2013?
>
> Sent from my iPhone
> Aaron M. Peck, SET Fire Protection
> Skype +1(202)407-9079
> Cambodia +855(0)78700407
>
> > On Feb 14, 2014, at 9:16 PM, John Denhardt <jdenha...@stricklandfire.com> 
> > wrote:
> >
> > Not with the 2013 edition of 13. Changed all steel pipping to 100 for dry 
> > and preaction systems.
> >
> > Thanks,
> > John August Denhardt P.E.
> >
> >> On Feb 14, 2014, at 9:06 AM, "Aaron Peck" <amp...@me.com> wrote:
> >>
> >> If you use black pipe is a reduction of your pipe C-Factor. I believe it's 
> >> reduced to 120... but I don't have the code in front of me.
> >>
> >> Galvanized pipe lets you retain you C-Factor.
> >>
> >> Sent from my iPhone
> >> Aaron M. Peck, SET Fire Protection
> >> Skype +1(202)407-9079
> >> Cambodia +855(0)78700407
> >>
> >>> On Feb 14, 2014, at 8:54 PM, John Denhardt <jdenha...@stricklandfire.com> 
> >>> wrote:
> >>>
> >>> Why will it not be allowed? No restrictions. Used to be done all the time 
> >>> especially with Navy projects.
> >>>
> >>> Thanks,
> >>> John August Denhardt P.E.
> >>>
> >>>> On Feb 14, 2014, at 7:27 AM, "James D. Waite" <jdwa...@flsamerica.com> 
> >>>> wrote:
> >>>>
> >>>> Didn't there used to be a section in 13 that specifically allowed black 
> >>>> steel fittings with galvanized pipe on dry systems? I've been looking 
> >>>> for a few days and haven't been able to find it.
> >>>>
> >>>> Jimmy Waite, CET - Design Manager Fire & Life Safety America-
> >>>> Raleigh District
> >>>> 7711 Welborn Street, Suite 103
> >>>> Raleigh, NC 27615
> >>>> Office: 919-872-3250
> >>>> Cell: 919-868-3546
> >>>> Fax: 919-877-5775
> >>>> www.flsamerica.com
> >>>>
> >>>> ________________________________
> >>>>
> >>>> The information contained in this email and any attached documents may 
> >>>> contain information that is the confidential property of Fire & Life 
> >>>> Safety America, Inc ("FLSA"). Any documents created on any FLSA computer 
> >>>> or by any employee in the conduct of FLSA business is work product and 
> >>>> owned by FLSA. If the reader of this message is not the intended 
> >>>> recipient, or the employee or agent responsible to deliver it to the 
> >>>> intended recipient, you are hereby notified that any dissemination, 
> >>>> distribution or other use of the contents of this communication is 
> >>>> strictly prohibited. If you have this communication in error, please 
> >>>> immediately notify the sender and delete this email.
> >>>> _______________________________________________
> >>>> Sprinklerforum mailing list
> >>>> Sprinklerforum@lists.firesprinkler.org
> >>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesp
> >>>> rinkler.org
> >>> _______________________________________________
> >>> Sprinklerforum mailing list
> >>> Sprinklerforum@lists.firesprinkler.org
> >>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firespr
> >>> inkler.org
> >> _______________________________________________
> >> Sprinklerforum mailing list
> >> Sprinklerforum@lists.firesprinkler.org
> >> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firespri
> >> nkler.org
> > _______________________________________________
> > Sprinklerforum mailing list
> > Sprinklerforum@lists.firesprinkler.org
> > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprin
> > kler.org
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org
>
> ________________________________
>
> The information contained in this email and any attached documents may 
> contain information that is the confidential property of Fire & Life Safety 
> America, Inc ("FLSA"). Any documents created on any FLSA computer or by any 
> employee in the conduct of FLSA business is work product and owned by FLSA. 
> If the reader of this message is not the intended recipient, or the employee 
> or agent responsible to deliver it to the intended recipient, you are hereby 
> notified that any dissemination, distribution or other use of the contents of 
> this communication is strictly prohibited. If you have this communication in 
> error, please immediately notify the sender and delete this email.
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org

_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

________________________________

The information contained in this email and any attached documents may contain 
information that is the confidential property of Fire & Life Safety America, 
Inc ("FLSA"). Any documents created on any FLSA computer or by any employee in 
the conduct of FLSA business is work product and owned by FLSA. If the reader 
of this message is not the intended recipient, or the employee or agent 
responsible to deliver it to the intended recipient, you are hereby notified 
that any dissemination, distribution or other use of the contents of this 
communication is strictly prohibited. If you have this communication in error, 
please immediately notify the sender and delete this email.
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to