NFPA 13, 2013 edition, 8.16.1.1.2.1 "Valves on connection to water supplies,
sectional control and isolation valves, and other valves in supply pipes to
sprinkler and other fixed water-based fire suppression systems shall be
supervised by one of the following methods:
(1) Central station, proprietary, or remote station signaling service
(2) Local signaling service that will cause the sounding of an audible
signal at a constantly attended point
(3) Valves locked in the correct position
(4) Valves located within fenced enclosures under the control of the
owner, sealed in the open position, and inspected weekly as part of an approved
procedure
I don't believe you would be required to electrically monitor or chain that
valve based on this section. FWIW, we always spec the valve on the backflow
test outlet piping to be supervised. Falls under the "good practice" category
in my opinion.
Nice to see someone providing means to full forward flow the backflow as
required.
Reed A. Roisum, C.E.T. | Karges-Faulconbridge, Inc. | Fire Protection Designer
| Fargo, ND | direct: 701.552.9903 | mobile: 701.388.1352 |
http://www.kfiengineers.com
-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of John
Denhardt
Sent: Monday, February 17, 2014 3:21 PM
To: [email protected]
Subject: RE: Butterfly valve, monitered or not?
Agree. However, this is similar to a fire pump test header control valve. The
NFPA 20 committee thought it was important enough to supervise the fire pump
test header valve. To me, this is a wasteful requirement but it is a
requirement. We need this requirement changed.
John
John August Denhardt, P.E., FSFPE
Strickland Fire Protection Incorporated
5113 Berwyn Road
College Park, Maryland 20740
Office Telephone Number: 301-474-1136
Mobile Telephone Number: 301-343-1457
FIRE SPRINKLERS SAVE LIVES - Can you live without them?
-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Brad
Casterline
Sent: Monday, February 17, 2014 4:07 PM
To: [email protected]
Subject: RE: Butterfly valve, monitered or not?
Douglas,
Search the archives for 'full forward flow test control valves'.
lots of good stuff and fairly recent.
brad
-----Original Message-----
From: Douglas Hicks [mailto:[email protected]]
Sent: Monday, February 17, 2014 2:58 PM
To: [email protected]
Subject: Butterfly valve, monitered or not?
I am going to install a 4" butterfly valve on a sprinkler manifold. This will
give us an outlet to perform a Forward Flow. Does the valve need to be
monitored or will it be OK to use a chain to lock the valve in the closed
position?
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com
______________________________________________________________________
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org