You're right Ron and John, just did one today on a test header and 2 turns
to signal supervisory on FA.
One additional location would be flushing valves.  I can't see the
feasibility of monitoring these.
TD


John's right. You need a valve with a switch that is meant to be normally
closed. I know Victaulic makes these and I suspect everyone else does also
though I couldn't testify to that in sprinkler court.



> Not allowed. Must pick up within two turns of normal position.  We did 
> it your way for years but new valves are made that comply with the
standard.
>
> Thanks,
> John August Denhardt P.E. 