>From my viewpoint.  We do not use 1.5 inch hose any more common around us
is 1.75 to get more water on fire quicker.
Norm
On Feb 19, 2014 8:51 AM, "Brad Casterline" <[email protected]> wrote:

> Does anyone know why the technical committee settled on 100 PSI minimum at
> the 2.5" hose valve?
>
> It used to be 75 PSI, and for High Rise retrofit I have seen AHJs accept
> 75.
>
> I am just curious because I think with about 60 PSI at the 2.5" connection
> to the standpipe we could get about 250 GPM at the nozzle, figuring the Pf
> for the T, 2.5x0-6 nip, hose valve, and 100 feet of 2.5" hose.
>
> A 15 psi safety factor seems reasonable, but 40 psi???
>
> I know the F.D. might want to use a 2.5x1.5 reducer and 1.5" hose, but with
> 150 GPM flowing through 100 feet of 1.5" hose the Pf in the hose alone is
> about 162 PSI!
>
> So, I don't get it, but I am likely missing some simple explanation, so I'm
> asking.
>
>
>
> thanks,
>
>
>
>
>
> Brad Casterline, NICET IV
>
> Fire Protection Division
>
>
>
> FSC, Inc.
>
> P: 913-722-3473
>
> [email protected]
>
> www.fsc-inc.com
>
>
>
> Engineering Solutions for the Built Environment
>
>
>