I've gone through much of his technical data and white papers, calling will be on the horizon. He helped me with an underwing AFFF system many years ago..
Thank you, Bob Knight, CET III 208-318-3057 www.firebyknight.com -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Roland Huggins Sent: Wednesday, February 26, 2014 12:41 PM To: [email protected] Subject: Re: AFFF Bladder Tank Sizing If you are using Viking equipment, call Martin Workman. It's worth climbing the mountain to talk to the Guru. Roland Roland Huggins, PE - VP Engineering American Fire Sprinkler Assn. --- Fire Sprinklers Saves Lives Dallas, TX http://www.firesprinkler.org On Feb 26, 2014, at 10:57 AM, Bob <[email protected]> wrote: > I have a NFPA 30 project where I need to size a bladder tank for 3% > AFFF solution. I have looked but can't find any info on sizing the > tank. I am assuming that I need to take the gpm flowing x .03 x 15 > min duration. The only thing I have found for a safety factor in in 409 where it uses 1.15. > For example, 750 gpm x .03 = 22.5 x 15 = 337.5 x 1.15 = 388.125 gal. > Does this sound right? > > > Thank you, > > Bob Knight, CET III > 208-318-3057 > www.firebyknight.com > > > > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl > er.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org