Thanks, Brad & Ron. I thought moving the heater may be the only answer. Though 
how you can do that with a 10'x10' ESFR spacing beats me.
Tony

----- Original Message -----
From: [email protected]
To: [email protected]
Sent: Thursday, February 27, 2014 6:55:11 AM
Subject: RE: ESFR sprinklers

There is really no reason to use 165's, we use only 212's. I'm not aware of any 
286F ESFR's but I haven't really look for them either. AFSA has great sprinkler 
head chart on their web site. And George was right, usually the unit heaters 
have to be moved because of the spacing limitations of ESFR's. It takes a lot 
of coordination early on in the project to prevent obstructions. We have the 
best results when we're on board before the structural design is completed.
Ron F

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Tony Silva
Sent: Wednesday, February 26, 2014 11:51 PM
To: [email protected]
Subject: ESFR sprinklers

Using k=25.2 ESFR sprinklers at the ceiling in a storage application 
calculating 12 heads as per NFPA 13,

(1) Can the heads be 165 deg.F or must they be 212 deg.F? (assuming no heat 
sources)
(2) If there is a heat source, such as a unit heater, are there ESFR heads 
rated for 286 deg.F? I see only 165 & 212.

Thanks,

Tony
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to