Show off...

Sent from my iPhone
Jamie Seidl 

> On Mar 13, 2014, at 2:30 PM, "rongreenman ." <[email protected]> wrote:
> 
> 1-8.1.1 in the 1977 edition.
> 
> 
> On Thu, Mar 13, 2014 at 11:15 AM, BJ Newlin <[email protected]>wrote:
> 
>> From the 2013 ed. of NFPA 2013
>> 
>> 
>> 6.2.1.1 When a sprinkler has been removed for any reason, it shall not be
>> reinstalled.
>> 
>> BJ Newlin
>> Service Sales
>> Aegis Fire Protection LLC.
>> 
>> "Whoever is careless with the truth in small matters cannot be trusted with
>> important matters"
>> -- Albert Einstein
>> 
>> 
>> 
>> -----Original Message-----
>> From: [email protected]
>> [mailto:[email protected]] On Behalf Of
>> [email protected]
>> Sent: Thursday, March 13, 2014 1:09 PM
>> To: [email protected]
>> Subject: Question on old sprinkler heads
>> 
>> Could anybody tell me where and if there is a code that says you have to
>> replace sprinkler heads with new ones once they are removed?
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> 
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>> 
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> 
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> 
> 
> 
> -- 
> Ron Greenman
> Instructor
> Fire Protection Engineering Technology
> Bates Technical College
> 1101 So. Yakima Ave.
> Tacoma, WA 98405
> 
> [email protected]
> 
> http://www.bates.ctc.edu/fireprotection/
> 
> 253.680.7346
> 253.576.9700 (cell)
> 
> Member:
> ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC
> 
> They are happy men whose natures sort with their vocations. -Francis Bacon,
> essayist, philosopher, and statesman (1561-1626)
> 
> A problem well stated is a problem half solved. -Charles F. Kettering,
> inventor and engineer (1876-1958)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org