Ladies & Gentlemen: We have run in to similar - not exact - circumstances on BIA Projects both here in NM and AZ. Long story short - BIA accepted/approved similar 'contradictory' design criteria when an engineering decision/judgement was made (i.e., plans/calc's 'sealed') by a licensed PE/FPE registered in State of project. Actually, we have previously gotten around 0.15/OH1 densities when our drawings were sealed by our FPE. Regards to All- Jerry [email protected]_ (mailto:[email protected]) Jerry D. Watts, SFPE President & Co-Founder ACCENT FIRE ENGINEERING INT'L. Ltd* Santa Fe/Albuquerque/Las Cruces/Silver City/Roswell/Artesia New Mexico Seattle, WA San Diego, CA Phoenix, AZ San Antonio, TX (800) 503.1961 nationwide *Licensed Fire Protection Engineers - Architects/Inspectors/Fire Investigators: AZ CA CO NM NV NY TX UT KS MD MS In a message dated 3/19/2014 1:03:59 P.M. Mountain Daylight Time, [email protected] writes:
We are looking at a project with the BIA (Bureau of Indian Affairs). They require all bldgs over 2000 sq ft to be Ord Grp I as a minimum in ALL areas. We have dealt with them in the past and there seems to be no waivering on this issue. We had a contractor in the past install Tyco BB heads and calc'd for 0.15 gpm. Tyco had written letters that calculating to 0.15 would be fine. But the data sheet for those heads says light hazard. So, the BIA rejected and the attic had to be re-piped for SSU for protection. Now, the current project has concealed combustible spaces requiring the specially listed heads for flat, shallow concealed combustible spaces - Tyco CC, Viking COIN, etc.. However, we are going to have the problem that these heads are listed for light hazard only. We can't go to SSU because NFPA 13 states that you must use specially listed heads for these concealed spaces. We are awaiting a response from the BIA, but I am not expecting much help. Have any of you ever run into this? If so, how did you address it? We can't use the only heads listed for the area because they are only listed as light hazard and the BIA requires all areas to be OH1 minimum. We can't use SSU sprinklers because NFPA 13 prohibits their use in these spaces. It is a true Catch 22. -- Travis Mack, SET MFP Design, LLC 2508 E Lodgepole Drive Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 email:[email protected] _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org