According to NFPA 13 2007 8.6.3.2.3, In a situation with angled and
irregular walls, you are allowed to go 75% of the maximum distance between
sprinklers provided the maximum perpendicular distance is not exceeded.  My
question is how do you actually figure the square footage required to do a
calculation?  For instance, if you look at the diagram in the appendix ,
what would be the square footage of that sprinkler? 

Would it be (2 x 7'6) x (2 x 11.25)?   Or (2 x 7'-6") x (11.25' x 1.333)
or just (2 x 7'6) x (2 x 7'6)?

 

 