Well if its light hazard I would point out to him that 8.6.5.2.2 would be
the applicable rule (if they are suspended from the ceiling), other than
that, the only other rules you can use are table 8.6.5.1.2 or 8.6.5.1.2 (2) 

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
Martinez, Dewayne
Sent: Monday, March 24, 2014 11:36 AM
To: SprinklerFORUM
Subject: NFPA 13 (07ed) 8.6.5.1

I have an AHJ telling me that a sprinkler must comply with both sections of
8.6.5.1.  The problem I am having is the he is telling me that the suspended
lights must comply with the table 8.6.5.1.2 (beam rule) because it is part
of 8.6.5.1 even though the edge of the lights are at least 24in away from
the sprinkler.  The beam rule would require them to be at least 3ft away to
comply.  Any good idea how to respond to this?

Thanks,

Dewayne 