I also remember this and Chet always talked about the closely spaced sprinkler 
test.  He was the reason behind the latest changed (2010?) which made closely 
spaced sprinklers only required when be they were being provided in lieu of 
fire ratings.

John

It should be recognized that the above is my opinion as a member of the NFPA 13 
technical committee, and has not been processed as a formal interpretation in 
accordance with the NFPA Regulations Governing Committee Projects and should 
therefore not be considered, nor relied upon, as the official position of the 
NFPA, nor any of their technical committees.


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Sprinkler 
Academy - C Bilbo
Sent: Wednesday, March 26, 2014 4:50 PM
To: [email protected]
Subject: RE: closely spaced sprinklers and draftstops at floor openings

Hi Matt,
IF (big ol' IF) I am not mistaken, Schirmer Engineering ran some tests (perhaps 
it was for or with GSA?) to demonstrate that the closely spaced sprinklers 
could be effective enough to eliminate a very expensive, automatic, sliding, 
fire door to cover the floor opening at an escalator.  There were many of these 
in the Sears Tower in Chicago and Chet Schirmer brought the idea to the 
attention of the NFPA 13 Committee.  I am not sure if this before or after he 
became chair of the NFPA 13 Installation Criteria Committee or the Correlating 
Committee.  

Chet was on the NFPA 13 Committee for more than 40 years.

It should be recognized that the above is my opinion as a member of the NFPA, 
and has not been processed as a formal interpretation in accordance with the 
NFPA Regulations Governing Committee Projects and should therefore not be 
considered, nor relied upon, as the official position of the the NFPA, nor any 
of their technical committees. 

Sincerely,


Cecil Bilbo 
Academy of Fire Sprinkler Technology
Champaign, IL
217.607.0325
www.sprinkleracademy.com

[email protected]

 

OUR STUDENTS SAVE LIVES!!



> From: [email protected]
> To: [email protected]
> Date: Wed, 26 Mar 2014 14:09:38 -0500
> Subject: closely spaced sprinklers and draftstops at floor openings
> 
> I had a customer ask about where the 6'-0" spaced sprinks and 18" draftstops 
> came from. Anyone know how this design came about (or where I could look for 
> info).
> 
> Thanks,
> 
> Matt Grisé PE*, LEED AP, NICET II  
> Sales Engineer 
> Alliance Fire Protection 
> 130 w 9th Ave.
> North Kansas City, MO 64116
> 
> *Licensed in KS & MO 
> 
> 913.888.0647 ph 
> 913.888.0618 f 
> 913.927.0222 cell 
> www. AFPsprink.com 
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
                                          
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to