Speaking of George,

Cathy was just in said to say hi to everyone.

Richard L. Mote
Design Manager
Rowe Sprinkler Systems, Inc.
7994 Route 522, Suite 1
PO Box 407
Middleburg, PA 17842
P 570-837-7647
F 570-837-6335

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of 
rongreenman .
Sent: Thursday, April 03, 2014 11:30 AM
To: [email protected]
Subject: Re: Steeply pitched roof

I'm going to George Church on you Cesar. When you want to change the topic of a 
thread in this Forum, please do not tag on to an existing thread on a different 
topic, like "Steeply Pitched Roofs" with a backflow question.
Start a new topic thread.


On Thu, Apr 3, 2014 at 8:19 AM, Cesar Lira <[email protected]> wrote:

> Hi, everybody.
>
> Where can I use or where INEED to use a back flow preventer there is 
> any rule for that???..
>
> Regards..
>
>
>
> -----Mensaje original-----
> De: [email protected]
> [mailto:[email protected]] En nombre de 
> Todd
> -
> Work
> Enviado el: jueves, 03 de abril de 2014 02:31 a.m.
> Para: [email protected]
> Asunto: Re: Steeply pitched roof
>
> I ran into this situation with a sanctuary in a historic church 
> several years back. The geometry was such that not all of the 
> requirements of NFPA
> 13 could be met. We handled this similar to what has been described here.
>
> Todd G Williams, PE
> Fire Protection Design/Consulting
> Stonington, CT
> www.fpdc.com
> 860-535-2080 (ofc)
>
> > On Apr 3, 2014, at 5:19 AM, "Dan Arbel" <[email protected]> wrote:
> >
> > Ronald,
> >
> > This is a very old provision.
> >
> > The sprinkler spray is clearly disturbed.
> >
> > Do you know if this provision is based on any test?
> >
> > Dan
> >
> >
> > www.riskmanage.com
> > Tel: 972-4-8243337,  972-777-504-011
> > Fax: 972-4-8243278,
> > [email protected]
> >
> > -----Original Message-----
> > From: [email protected]
> > [mailto:[email protected]] On Behalf Of 
> > Roland Huggins
> > Sent: Wednesday, April 02, 2014 11:26 PM
> > To: [email protected]
> > Subject: Re: Steeply pitched roof
> >
> > I would not focus on the phrase shall be permitted (which taken by 
> > itself means optional).  I would focus on the portion that states to 
> > maintain a horizontal distance of 24 inches.  Combine this with 
> > Figure
> > 8.6.4.1.3.3 that dictates the 4 ft separation is a minimum leads to 
> > the interpretation that you must be 2 ft away on each side and you 
> > are
> allowed to exceed the 36"
> > vertical maximum to accomplish it.
> >
> > Roland
> >
> >
> > Roland Huggins, PE - VP Engineering
> > American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves Lives
> > Dallas, TX
> > http://www.firesprinkler.org
> >
> >
> >
> >
> >
> >> On Apr 2, 2014, at 11:17 AM, Juan Munguia 
> >> <[email protected]>
> wrote:
> >>
> >> My opinion is section 8.6.4.1.3.3 requires a minimum horizontal 
> >> clearance of 24 inches, and therefore allows the deflector to be 
> >> located at a vertical distance greater than 36 inches down from the
> peak.
> >>
> >> Juan Munguia
> >
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprin
> > kl
> > er.org
> >
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprin
> > kl
> > er.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org
>



--
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC

They are happy men whose natures sort with their vocations. -Francis Bacon, 
essayist, philosopher, and statesman (1561-1626)

A problem well stated is a problem half solved. -Charles F. Kettering, inventor 
and engineer (1876-1958) _______________________________________________