NFPA 13, 2010 edition: 8.6.4.1.1.1

1" min / 12" max.

Travis Mack, SET
MFP Design, LLC
2508 E Lodgepole Drive
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
email:[email protected]

On 4/14/2014 4:47 PM, [email protected] wrote:
standard spray unobstructed
In a message dated 4/14/2014 7:44:55 P.M. Eastern Daylight Time,
[email protected] writes:

standard  spray or sidewall or residential pendent or ???? Obstructed or
unobstructed construction??

Travis Mack, SET
MFP Design,  LLC
2508 E Lodgepole Drive
Gilbert, AZ 85298
480-505-9271
fax:  866-430-6107
email:[email protected]

On 4/14/2014 4:42 PM,  [email protected] wrote:
What is the maximum allowable distance a  sprinkler head can be below a
ceiling. I believe it is 12". Can  anybody confirm?
Thanks