We have a project with something I don’t think I have seen
before.2x6 Wood roof joists with plywood on top.2x6 ceiling joists, except they 
decided not to put a sheet
rock ceiling below the ceiling joists. We now have sprinklers below the roof 
joists, which will be
about 3’ above the ceiling joists. We would have had sprinklers below the 
ceiling, but now,
they would not work below the open wood joists. Do we have proper protection
with just the sprinklers at the roof? (NFPA #13 – 2013) Section 8.15.14 looks 
like it is OK with
just the roof joists, with a maximum of 10’ x 12’ spacing. 



















Is this correct?