I would say that if the garages are for resident use only and they are 
ancillary to the primary occupancy, then you could use 13R

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860-535-2080
www.fpdc.com


> On Apr 22, 2014, at 1:17 AM, George Medina Jr <[email protected]> wrote:
> 
> 
> 
> Forum,
> Can anyone please add there 2 cents in and help clarify when to classify as a 
> 13 system versus a 13R
> I have a project that consist of 3 stories with an occupancy of R2/S2 and 
> Construction Type VA. The project is lay ed out like a horse shoe
> with 3 sides  and a corridor running down the middle from  1 required 
> stairwell to another on the opposite end, with a court yard in the middle. 
> There are private garages around the perimeter of the building (which all 
> have access from a common 1st floor corridor only) All the Garages have a 2 
> hour separation between them and the 2nd level  residential units and the 1st 
> floor corridor. There are residential units on the 1st floor (opposite the 
> garages) facing the court yard.
> 
> I figured the Garage calculations shall conform to NFPA-13, based on NFPA-13R 
> (2013ed.) Sec. 7.3.1. My question is if the building can be classified as a 
> 13R (with garage areas calced at NFPA-13) or should it be classified as a 
> NFPA-13 with dwelling units & residential heads (calculations based on the 
> greater of the area/density @ .10 or the head listing). If not, what is the 
> determining factor or the threshold.
> 
> 
> 
> 
> 
> George Medina Jr. 
> Mobile: 323-906-5701
> 
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to