I looked and didn’t see a data sheet specifically for esfr (storage in their 
terminology). Did go through data sheet 8-9 (storage of class 1-4) but didn’t 
see anything that special to FM. Thanks.

Rod at Rapid

From: Matthew Willis [mailto:[email protected]]
Sent: Tuesday, May 13, 2014 10:45 AM
To: Rod DiBona
Cc: [email protected]
Subject: Re: esfr FM Global

Get the FM data. They have "confidential" in house documents that sometimes 
exceed what we think of as norm. Like going from 12 to more flowing, higher end 
head etc. Learned this on a tissue paper project one time.

R/
Matt

On Tue, May 13, 2014 at 12:42 PM, Rod DiBona 
<[email protected]<mailto:[email protected]>> wrote:
I am wondering if there are any major issues to watch for when bidding an ESFR 
(FM = Storage sprinkler) to meet FM rather than NFPA? The only things that come 
to mind is the 12 head calc not 14. Starting head Psi looks like 50 for FM 
compared to 52 for NFPA. Not wanting anybody to look anything up or spend 
anytime on this. Just wondering if there is anything obvious that I need to be 
looking out for? Thanks!

Rod at Rapid