That brings up the question. Is this exhauster installed at the pre-action valve or at the end of the line? If at the end of line and it is installed according to Star's data sheet there are a couple of 1/2" circle seal check valves that are very prone to clogging. Also check out the strainer that should be installed upstream of the exhauster if it is plugged it's game over. One last place to check is the 2" outlet valve on the bottom of the strainer. Remove the three hex head bolts and pull out the plug, there are two fine mesh screens held in place by a single bolt and a brass spacer. If they clog, again game over. If needs be contact me off forum and I will try to help you. I wrote and illustrated the data sheet for the BB-Exhauster when I worked for Star.
Richard Mote ET Designer Rowe Sprinkler Systems, Inc. PO Box 407 Middleburg, PA 17842 P- 877-324-ROWE F- 570-937-6335 [email protected]<mailto:[email protected]> www.rowesprinkler.com<http://www.rowesprinkler.com> _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org