Thank you.  That was really bugging me.

On Fri, Jun 6, 2014 at 8:41 AM, B.J. Newlin <[email protected]>
wrote:

> You are not required to include them.  From the 2013 ed.
>
> 23.4.4.6.3 The requirements of 23.4.4.6.1.1 to include every
> sprinkler in the design area shall not apply where spray sprinklers
> or CMSA sprinklers are provided above and below obstructions
> such as wide ducts or tables.
>
> B.J. Newlin
> Service Sales
> Aegis Fire Protection LLC.
>
> "Whoever is careless with the truth in small matters cannot be trusted with
> important matters"
> ― Albert Einstein
>
>
>
>
> -----Original Message-----
> From: Sprinklerforum [mailto:
> [email protected]]
> On Behalf Of Jamie Seidl
> Sent: Friday, June 06, 2014 7:37 AM
> To: [email protected]
> Subject: Sprinklers under duct
>
> I seem to be drawing a blank and also can not find it in the standard, so
> if
> someone can tell me off the top of their head, I'd appreciate it.
> Are standard spray sprinklers located under obstructions greater than 4'
> required to be included in calculations?  I seem to remember, no they are
> not, however the reference in the standard is eluding me.
>
> Thanks,
> Jamie Seidl
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>



-- 
     \ \
     (o>  --  If life were easy...
 \ \_/ /)                           It'd be called your mom...
  \_/_)
   _|_
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to