Thank you. That was really bugging me.
On Fri, Jun 6, 2014 at 8:41 AM, B.J. Newlin <[email protected]> wrote: > You are not required to include them. From the 2013 ed. > > 23.4.4.6.3 The requirements of 23.4.4.6.1.1 to include every > sprinkler in the design area shall not apply where spray sprinklers > or CMSA sprinklers are provided above and below obstructions > such as wide ducts or tables. > > B.J. Newlin > Service Sales > Aegis Fire Protection LLC. > > "Whoever is careless with the truth in small matters cannot be trusted with > important matters" > ― Albert Einstein > > > > > -----Original Message----- > From: Sprinklerforum [mailto: > [email protected]] > On Behalf Of Jamie Seidl > Sent: Friday, June 06, 2014 7:37 AM > To: [email protected] > Subject: Sprinklers under duct > > I seem to be drawing a blank and also can not find it in the standard, so > if > someone can tell me off the top of their head, I'd appreciate it. > Are standard spray sprinklers located under obstructions greater than 4' > required to be included in calculations? I seem to remember, no they are > not, however the reference in the standard is eluding me. > > Thanks, > Jamie Seidl > _______________________________________________ > Sprinklerforum mailing list > [email protected] > > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org > -- \ \ (o> -- If life were easy... \ \_/ /) It'd be called your mom... \_/_) _|_ _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org