How are the sprinkler mains configured after the stand pipe bulk main branches 
off?


SteveĀ 

<div>-------- Original message --------</div><div>From: "Martinez, Dewayne" 
<[email protected]> </div><div>Date:06/06/2014  6:43 AM  
(GMT-08:00) </div><div>To: [email protected] 
</div><div>Subject: control valve on standpipe bulk main? </div><div>
</div>NFPA 13 or 14 (07ed)

Situation:

Water supply with BFP supplying one wet system and one standpipe system.
Wet system has a control valve in the riser room but we would like not
to put a control valve on the standpipe riser / bulk main in order to
connect the FDC to it father down in the building.  Each stairwell
standpipe will have  a control valve to isolate it off the standpipe
bulk main.  AHJ is requiring an additional control valve on the bulk
main in the riser room which would require us to now run an additional
250ft of 4in pipe to the FDC location.  Of course he won't state where
he gets this requirement just that he wants it.  I have piped several
buildings this way in the past.  Have I been doing it wrong all these
years?