I have always been under the impression that the safety factor indicated in
specifications for hydraulic calculations was for water supply fluctuations
in sprinkler systems connected to public water supplies. This is also
indicated in the commentary in the NFPA 13 Handbook.

However, recently a sprinkler contractor was contending that it was to
allow for field piping changes.

Any opinions?

 *Thanks*

*Rahe Loftin, PE  *